2003 IBC
This is one to name a few.
506.3. For Group R buildings equipped throughout with an approved
automatic
sprinkler system in accordance with Section 903.3.1.2, the value
specified
in Table 503 for maximum height is increased by 20 feet (6096 mm)
and the
maximum number of stories is increased by one story, but shall not
exceed
four stories or 60 feet (18 288 mm), respectively.
Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
[EMAIL PROTECTED]
www.burtellfire.com
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron
Greenman
Sent: Friday, February 09, 2007 3:31 PM
To: [email protected]
Subject: Re: Residential Trade-offs?
Note change of topic.
Joe,
I thought there were no I Code trade-offs that allowed for 13R. I'd
love to be educated if you can expand on your comment.
On 2/9/07, Joe Burtell <[EMAIL PROTECTED]> wrote:
> It will depend on the exceptions the architect took for trade-
offs. Some
of
> the trade-offs allow you to install per 13 or 13R, some only
allow 13. Did
> he take any trade-offs?
>
> Joe Burtell, SET, CFPS
> Burtell Fire Protection, Inc.
> [EMAIL PROTECTED]
> www.burtellfire.com
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of
George
Church
> Sent: Friday, February 09, 2007 2:06 PM
> To: [email protected]
> Subject: Residential?
>
>
> We have a project in which the majority of the building is dorm
rooms;
> 2nd flr (top) is all dorms, with a few more dorm rooms and a few
classrooms
> and offices on the first floor. Small basement is mechanical only.
> Entire building footprint is a whopping
>
> The classrooms are for the use of the students that reside in
the dorm;
> Offices for faculty that teach there.
>
> Overall concept is suburban campus college has this building in
the city
for
> students to study government and urban life. So the non-
residential areas
> are incidental to the residential nature of the building.
>
> The Architect has deemed the building A3 for the first floor, R2
on 2nd
> floor. Naturally the one hour separation is at the first floor
ceiling.
>
> If this sounds a little strange, at least it's not #13TR,
elderly housing
> over tire storage:) This IS located in a locale where 13d tank/
pumps feed
3
> story office buildings, with poly tanks located in restaurant
storage
area,
> and CPVC in OH2. Sure, that will make the judge understand ?
>
> Anyway, would % of use and other uses being for the occupants
make this
look
> #13R to any of you?
>
> George Church
> Rowe Sprinkler
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum