Todd:
   
  For fittings that aren't in 13, I always refer to the Crane Company piping 
manual.  In their table of fittings and valves, an 2-1/2 inch angle valve is 
equivalent to 33 feet of 2-1/2 inch steel pipe.  So at a flow of 250 gpm, you 
lose about 7 psi.
   
  If you want a copy of the table, contact me off-line with a fax number and I 
will send it to you.

  Dave
   
  David de Vries, P.E., CSP
  [EMAIL PROTECTED]
  
Todd Williams - work <[EMAIL PROTECTED]> wrote:
  Someone in the Forum recently made a reference to friction loss in 
fire hose valves being around 3 psi with some higher. Is there any 
documentation for that? I haven't be able to locate any. Thanks.

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com 

_______________________________________________