Todd:
   
  For fittings that aren't in 13, I always refer to the Crane Company
piping manual.  In their table of fittings and valves, an 2-1/2 inch
angle valve is equivalent to 33 feet of 2-1/2 inch steel pipe.  So at a
flow of 250 gpm, you lose about 7 psi.
   
  If you want a copy of the table, contact me off-line with a fax number
and I will send it to you.

  Dave
   