We had a utility deem their supply unreliable at the last minute and the local AHJ and our FPE to agreed that, with some controller mods for slightly delayed start, a natural gas fired generator could be used as the SOLE source of power. The local AHJ deemed the natural gas supply to be reliable.
Kudos for the Joslyn-Clark rep and factory that resolved the necessary mods, assisted with approvals, and had it onsite in a week- out Fri PM for a Sat AM delivery onsite, acceptance test Monday. Some days you need supportive vendors and professionals that can jump thru hoops ! glc -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams - work Sent: Friday, February 16, 2007 9:39 AM To: [email protected] Subject: back-up power I am working on a project where an electric fire pump (diesel not an option) and tank is the only source of water for the sprinkler system. The primary supply is the public utility and the back-up is to come from an on-site generator. The builder is proposing to use a propane-fired generator. I looked in NFPA 20 and 110 and didn't see anything saying this was a no-no. Is there a problem with this arrangement? Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut 860-535-2080 www.fpdc.com _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum