How does the propane supplier differ from the diesel fuel supplier??
Are diesel suppliers somehow more reliable in an emergency? 

NFPA 70 says that the prime mover shall not be solely dependant upon a
"public utility" for their fuel supply.  Joe's propane delivery is not a
public utility.  I can understand the not relying on a public utility
that may be subject to the same event that interrupted the electric
supply to begin with (e.g. both utilities damaged by an earthquake). 

Paul J. Pinigis, P.E.
Chief Life Safety Engineer


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Friday, February 16, 2007 1:07 PM
To: [email protected]
Subject: Re: back-up power

Propane supplier or local gas company -  a gas fired generator is solely
dependent on a gas system for their fuel supply. - These are typically
considered unreliable during an emergency

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- 
From: "Paul Pinigis" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Friday, February 16, 2007 9:51 AM
Subject: RE: back-up power


I do not see this prohibition in the NEC. The closest that I find is
that prime movers shall not be solely dependent on a public utility gas
system for their fuel supply.  This does not mean that they cannot be
powered by gas.

Which section of the NEC are you referring to?

Paul J. Pinigis, P.E.
Chief Life Safety Engineer


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Friday, February 16, 2007 11:31 AM
To: [email protected]
Subject: Re: back-up power

The NEC doesn't allow life safety systems to operate of a gas fired
generator.  You need local AHJ approval to use them.


Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- 
From: <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Friday, February 16, 2007 8:35 AM
Subject: RE: back-up power


Why propane versus the more common and probably cheaper diesel?
Environmental issues, i.e. exhaust?

Is your primary power source considered non-reliable thus necessitating
a secondary backup source?


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - work
Sent: Friday, February 16, 2007 9:39 AM
To: [email protected]
Subject: back-up power

I am working on a project where an electric fire pump (diesel not an
option) and tank is the only source of water for the sprinkler system.
The primary supply is the public utility and the back-up is to come from
an on-site generator. The builder is proposing to use a propane-fired
generator. I looked in NFPA 20 and 110 and didn't see anything saying
this was a no-no. Is there a problem with this arrangement?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
************************************************************************
**********************
IMPORTANT: The contents of this email and any attachments are
confidential. 
They
are intended for the named recipient(s) only.
If you have received this email in error, please notify the system
manager 
or the
sender immediately and do not disclose the contents to anyone or make
copies
thereof.
************************************************************************
**********************

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
**********************************************************************************************
IMPORTANT: The contents of this email and any attachments are confidential. 
They 
are intended for the named recipient(s) only.
If you have received this email in error, please notify the system manager or 
the 
sender immediately and do not disclose the contents to anyone or make copies 
thereof.
**********************************************************************************************

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to