I think the answer is found in the building code, not NFPA 13. When I
started the trade I knew nothing about the building code let alone owned
one. Now I don't know how you can even design without one and I wonder if a
few architect and engineers even look at it. The porte cochere is most
likely a utility or Group U occupancy. From the 03' IBC 

"312.1 General. Buildings and structures of an accessory character and
miscellaneous structures not classified in any specific occupancy shall be
constructed, equipped and maintained to conform to the requirements of this
code commensurate with the fire and life hazard incidental to their
occupancy. Group U shall include, but not be limited to, the following:
Agricultural buildings
Aircraft hangars, accessory to a one- or two-family
residence (see Section 412.3)
Barns
Car ports
Fences more than 6 feet (1829 mm) high
Grain silos, accessory to a residential occupancy
Green houses
Live stock shelters
Private garages
Retaining walls
Sheds
Stables
Tanks
Towers"

Your situation I would think would be a car port. That being said I see it
as a separate building or structure and sprinkler protection is not required
whether it's combustible or not unless there is something in the IBC about
proximity and exposure to the main structure. I think it's best left up to
the Building code official. If it can be shown in the code where sprinklers
are required for the accessory structure. Just my opinion.

Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
[EMAIL PROTECTED]
www.burtellfire.com
 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Rod DiBona
Sent: Friday, March 02, 2007 9:06 AM
To: [email protected]
Subject: RE: Porte cocheres

That is what I am trying to find Craig. At what point do we still have
to sprinkler a detached porte cochere. I can't find a definition in NFPA
or the IBC that describes a porte cochere to see if it is by definition
attached. What if it is 30' from the motel do we still have to sprinkler
it? I don't think so....I studied NFPA 8.15.7.1 thru 8.15.7.5 but now I
am thinking that those references are talking about when the "porte
cochere" is attached. Obviously an exterior roof and the canopy are
attached so why would this standard in the same section apply to another
structure that is not. If it is a separation issue I would like to know
where the line is drawn...3ft, 10ft, 40ft?? Hmmm. I will be looking at
the IBC. Any thoughts? Thanks.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Friday, March 02, 2007 6:32 AM
To: [email protected]
Subject: RE: Porte cocheres

Ruling we had was that combustible then sprinkle.  If not combustible we
did not have to sprinkle as long as the cars were there only temporarily
for pickup or drop off, not long term parking.

If yours is detached and combustible he could be citing separation
issues as listed in the IBC that can dictate the need for sprinklers in
the PC.


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Rod
DiBona
Sent: Thursday, March 01, 2007 6:20 PM
To: [email protected]
Subject: Porte cocheres

Is there any clear cut building code or nfpa standard that addresses
sprinklering porte cocheres?(normally the drive under entrance for
motels) I had the understanding that if they are attached and
combustible they needed to be covered but if they weren't BOTH that they
didn't. I have an "unattached" combustible porte cochere at a motel
where the fire marshal has asked us to sprinkler it from the dry system
in the attic. Thank you for your input.

Rod DiBona
Rapid Fire Protection

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to