If the AHJ is  classifying the PC as IBC group U which states that the
accessory structure meet the same requirements as the building they are
attached to.  If he uses that logic then if the main building would
require sprinklers based on the combustible type of construction, so
should the PC.

If you look in IBC 2003 for example, in chapter 6, table 602 it
references separation distances.  When you can not or don't meet those
distances you are generally required to provide sprinkler protection for
both buildings.  There are also some exceptions based on the hazard
produced by the exposing structure to the exposed structure.  This is a
REALLY brief look at this issue.  It can get a bit sticky when the
building types are not represented in  black and white within the code.

I would ask him for code references that he is applying to this
situation.  Sometimes things get interpreted incorrectly or just don't
apply. If you ask him for the info based on the premise that you need to
request a change order and the owner is needing documented reasons for
the request, he should be more than willing to help you out.  It so much
depends on what code sections he's applying and how he has interpreted
them.


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Rod
DiBona
Sent: Friday, March 02, 2007 11:06 AM
To: [email protected]
Subject: RE: Porte cocheres

That is what I am trying to find Craig. At what point do we still have
to sprinkler a detached porte cochere. I can't find a definition in NFPA
or the IBC that describes a porte cochere to see if it is by definition
attached. What if it is 30' from the motel do we still have to sprinkler
it? I don't think so....I studied NFPA 8.15.7.1 thru 8.15.7.5 but now I
am thinking that those references are talking about when the "porte
cochere" is attached. Obviously an exterior roof and the canopy are
attached so why would this standard in the same section apply to another
structure that is not. If it is a separation issue I would like to know
where the line is drawn...3ft, 10ft, 40ft?? Hmmm. I will be looking at
the IBC. Any thoughts? Thanks.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Friday, March 02, 2007 6:32 AM
To: [email protected]
Subject: RE: Porte cocheres

Ruling we had was that combustible then sprinkle.  If not combustible we
did not have to sprinkle as long as the cars were there only temporarily
for pickup or drop off, not long term parking.

If yours is detached and combustible he could be citing separation
issues as listed in the IBC that can dictate the need for sprinklers in
the PC.


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Rod
DiBona
Sent: Thursday, March 01, 2007 6:20 PM
To: [email protected]
Subject: Porte cocheres

Is there any clear cut building code or nfpa standard that addresses
sprinklering porte cocheres?(normally the drive under entrance for
motels) I had the understanding that if they are attached and
combustible they needed to be covered but if they weren't BOTH that they
didn't. I have an "unattached" combustible porte cochere at a motel
where the fire marshal has asked us to sprinkler it from the dry system
in the attic. Thank you for your input.

Rod DiBona
Rapid Fire Protection

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to