Chris,

They would have the same effect that any valve or fitting would have on the ability of a sprinkler system to function properly. The loss in pressure due to friction at various flows through the meters is required to be accounted for in the hydraulic calculations. Interestingly enough, NFPA-13D tells us that the actual chart loss from the meter manufacturer should be reviewed during the calculation process. If the chart loss is lower than those figures in the table in 13D it may be used, however the standard also says that if the chart loss from the manufacturer is greater than those shown in the table that the higher value MUST be used.

Out here we see hundreds of residential sprinklers systems every month, and for the most part they utilize 1" meters. With a 13 gpm demand per sprinkler, and a 5 gpm allowance for domestic use, the system flow of 31 gpm exceeds the values shown in 13D as acceptable for a 5/8", and is right on the line at the maximum allowed for a 3/4". There has been much shouting regarding the issue of meter size out here, and most of it accompanied by vague suggestions of dire consequences and thousands of dollars needlessly wasted if one position or another isn't followed.

What is your take on the issues involved?

PARSLEY CONSULTING

Ken Wagoner, SET

760.745.6181 voice

760.745.0537 fax

[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail

www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website




Chris Brown wrote:
Question to the forum:
What effect does a 5/8 inch or 3/4 inch water meter have on fire sprinkler 
system installed in an NFPA 13D or NFPA 13R system. The issue is one of the 
maximum continuous flow thru the meter and its effect on the ability of the 
fire sprinkler system to operate as intended. I respectfully request, Please 
research and answer after you have visited with the water meter manufacturer's 
and or water departments as I have already done. Keep in mind that a single 
residential sprinkler has a minimum of some where between 19 and 25 gpm 
requirements and that most dwellings have two sprinklers flowing in the 
hydraulically remote area.
This will be fun for a Friday:)

Thank you,

Chris Brown
Fire Protection Designer
Please note our new company name, e-mail address and web site.

innovative leader    $B"%(J     trusted partner

19910 West 161st Street Olathe, KS 66062 Office: 913.829.8650

Direct:
Cell: Fax:

913.747.2056
913.208.3600
913.829.8690

www.poolefire.com <http://www.poolefire.com/> Office Map <http://www.mapquest.com/maps/map.adp?address=19910%20W%20161st%20St&city=Olathe&state=KS&zipcode=66062-2700&country=US&title=%3cb%3e19910%20W%20161st%20St%3c/b%3e%3cbr%20/%3e%20Olathe,%20KS%2066062-2700,%20%20US&cid=lfmaplink2&name=>
This e-mail, and any files transmitted with it, are confidential and intended 
solely for the use of the individual or entity to which they are addressed.  If 
you have received this e-mail in error, please notify [EMAIL PROTECTED]

------------------------------------------------------------------------

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
------------------------------------------------------------------------

No virus found in this incoming message.
Checked by AVG Free Edition.
Version: 7.5.446 / Virus Database: 268.18.8/714 - Release Date: 3/8/2007 10:58 
AM

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to