Also watch out for meter setters. That is that serpentine piping that
raises the pipe up to just below grade so the meter is accesible. They
come with full flow valves or corp valves. The first is fine. The
second can rob you of psi in double digits.

On 3/9/07, PCE <[EMAIL PROTECTED]> wrote:wo
Chris,

They would have the same effect that any valve or fitting would have on
the ability of a sprinkler system to function properly.  The loss in
pressure due to friction at various flows through the meters is required
to be accounted for in the hydraulic calculations.  Interestingly
enough, NFPA-13D tells us that the actual chart loss from the meter
manufacturer should be reviewed during the calculation process.  If the
chart loss is lower than those figures in the table in 13D it may be
used, however the standard also says that if the chart loss from the
manufacturer is greater than those shown in the table that the higher
value MUST be used.

Out here we see hundreds of residential sprinklers systems every month,
and for the most part they utilize 1" meters.  With a 13 gpm demand per
sprinkler, and a 5 gpm allowance for domestic use, the system flow of 31
gpm exceeds the values shown in 13D as acceptable for a 5/8", and is
right on the line at the maximum allowed for a 3/4".

There has been much shouting regarding the issue of meter size out here,
and most of it accompanied by vague suggestions of dire consequences and
thousands of dollars needlessly wasted if one position or another isn't
followed.

What is your take on the issues involved?

PARSLEY CONSULTING

Ken Wagoner, SET

760.745.6181 voice

760.745.0537 fax

[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail

www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website




Chris Brown wrote:
> Question to the forum:
> What effect does a 5/8 inch or 3/4 inch water meter have on fire sprinkler 
system installed in an NFPA 13D or NFPA 13R system. The issue is one of the 
maximum continuous flow thru the meter and its effect on the ability of the fire 
sprinkler system to operate as intended. I respectfully request, Please research 
and answer after you have visited with the water meter manufacturer's and or water 
departments as I have already done. Keep in mind that a single residential 
sprinkler has a minimum of some where between 19 and 25 gpm requirements and that 
most dwellings have two sprinklers flowing in the hydraulically remote area.
>
> This will be fun for a Friday:)
>
> Thank you,
>
> Chris Brown
> Fire Protection Designer
> Please note our new company name, e-mail address and web site.
>
>
>
> innovative leader    ▲     trusted partner
>
> 19910 West 161st Street
> Olathe, KS  66062
> Office:  913.829.8650
>
> Direct:
> Cell:
> Fax:
>
> 913.747.2056
> 913.208.3600
> 913.829.8690
>
> www.poolefire.com <http://www.poolefire.com/>
> Office Map 
<http://www.mapquest.com/maps/map.adp?address=19910%20W%20161st%20St&city=Olathe&state=KS&zipcode=66062-2700&country=US&title=%3cb%3e19910%20W%20161st%20St%3c/b%3e%3cbr%20/%3e%20Olathe,%20KS%2066062-2700,%20%20US&cid=lfmaplink2&name=>
>
> This e-mail, and any files transmitted with it, are confidential and intended 
solely for the use of the individual or entity to which they are addressed.  If 
you have received this e-mail in error, please notify [EMAIL PROTECTED]
>
>
>
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> ------------------------------------------------------------------------
>
> No virus found in this incoming message.
> Checked by AVG Free Edition.
> Version: 7.5.446 / Virus Database: 268.18.8/714 - Release Date: 3/8/2007 
10:58 AM
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum



--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to