I agree again Ken. My experience with the water districts I have to
contend with is that they will install the meter they like and not the
one being used in other jurisdictions. It is all driven by the cost of a
meter at the time they purchase them and the cheapest manufactured meter
they can purchase from their vendor usually wins and how it will affect
a potential fire sprinkler system in a dwelling is not a factor.
Unfortunately for me the water meters being used in the area's I'm
concerned with don't have the characteristics of the Badger. I
appreciate your response. It should be known, I am a very strong
advocate of the NFPA 13D and NFPA 13R systems. I'm looking for help with
this issue and I'm hopeful and looking for that warm and fuzzy response
that says, "Its okay Chris"!!!!


Thank you,

Chris Brown
Fire Protection Designer, Poole Fire Protection
Office: 913.829.8650   Direct: 913.747.2056   Cell: 913.208.3600   Fax:
913.829.8690


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of PCE
Sent: Friday, March 09, 2007 1:01 PM
To: [email protected]
Subject: Re: Pandora's Box

Chris,

Badger makes a meter, model M40, which is 3/4 x 3/4, and their chart
shows that it can accept flows of up to 35 gpm.  And, at that flow, it
has a pressure loss of around 6.5 to 7.0 psi.  I would think that would
certainly be sufficient to not impact the design of a residential system
at the same level as the chart losses shown in NFPA-13D. 

Out here, the AHJ's are starting to require the designers [sue me if you
don't like that word] to submit the data on the meter along with the
calculations and plans.

Just one more item to check prior to submittal.

PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website




Chris Brown wrote:
> Thank you for the information and now we have another manufacturer a 
> meter of with the same results as described in my last email, a 5/8 
> inch or 3/4 inch will not meet the flow requirements of a lot of the 
> NFPA 13D and NFPA 13R systems. IF as the AHJ, designer or installer of

> such systems you should be thinking pretty hard right now.
>
>
> Thank you,
>
> Chris Brown
> Fire Protection Designer, Poole Fire Protection
> Office: 913.829.8650   Direct: 913.747.2056   Cell: 913.208.3600
Fax:
> 913.829.8690
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Kathryn

> Tyler
> Sent: Friday, March 09, 2007 11:40 AM
> To: [email protected]
> Subject: RE: Pandora's Box
>
> This is the water meter we use here a lot.
> http://www.badgermeter.com/pdf/recdisk/tech/rd-t-34.pdf
>
> http://www.vikinggroupinc.com/databook/sprinklers/residential/103105.p
> df is an example of a concealed head that could work with up to 16x16 
> spacing (flat ceilings only though - if on sloped clgs, the press.
> requirement goes way up) There are others that will work, but this is 
> an example. Generally, it is tough to go more than 16x16 spacing with 
> a 3/4" meter, unless the run of copper between the tap and meter is 
> very short, the water pressure is very high. (Don't forget the loss 
> through the pipe between the tap and meter must be included in the 
> calcs) Many have requested for only 1" meters to be installed now, 
> which is a lot more expensive.
> Kathryn
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of PCE
> Sent: Friday, March 09, 2007 8:48 AM
> To: [email protected]
> Subject: Re: Pandora's Box
>
> Chris,
>
> They would have the same effect that any valve or fitting would have 
> on the ability of a sprinkler system to function properly.  The loss 
> in pressure due to friction at various flows through the meters is 
> required to be accounted for in the hydraulic calculations.  
> Interestingly enough, NFPA-13D tells us that the actual chart loss 
> from the meter manufacturer should be reviewed during the calculation 
> process.  If the chart loss is lower than those figures in the table 
> in 13D it may be used, however the standard also says that if the 
> chart loss from the manufacturer is greater than those shown in the 
> table that the higher value MUST be used.
>
> Out here we see hundreds of residential sprinklers systems every 
> month, and for the most part they utilize 1" meters.  With a 13 gpm 
> demand per sprinkler, and a 5 gpm allowance for domestic use, the 
> system flow of 31 gpm exceeds the values shown in 13D as acceptable 
> for a 5/8", and is right on the line at the maximum allowed for a
3/4".
>
> There has been much shouting regarding the issue of meter size out 
> here, and most of it accompanied by vague suggestions of dire 
> consequences and thousands of dollars needlessly wasted if one 
> position or another isn't followed.
>
> What is your take on the issues involved?
>
> PARSLEY CONSULTING
>
> Ken Wagoner, SET
>
> 760.745.6181 voice
>
> 760.745.0537 fax
>
> [EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
>
> www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
>
>
>
>
> Chris Brown wrote:
>   
>> Question to the forum:
>> What effect does a 5/8 inch or 3/4 inch water meter have on fire 
>> sprinkler
>>     
> system installed in an NFPA 13D or NFPA 13R system. The issue is one 
> of the maximum continuous flow thru the meter and its effect on the 
> ability of the fire sprinkler system to operate as intended. I 
> respectfully request, Please research and answer after you have 
> visited with the water meter manufacturer's and or water departments 
> as I have already done. Keep in mind that a single residential 
> sprinkler has a minimum of some where between 19 and 25 gpm 
> requirements and that most dwellings have two sprinklers flowing in
the hydraulically remote area.
>   
>>  
>> This will be fun for a Friday:)
>>
>> Thank you,
>>
>> Chris Brown
>> Fire Protection Designer
>> Please note our new company name, e-mail address and web site.
>>
>>  
>>
>> innovative leader    $B"%(J     trusted partner
>>
>> 19910 West 161st Street
>> Olathe, KS  66062
>> Office:  913.829.8650
>>
>> Direct:
>> Cell: 
>> Fax:
>>
>> 913.747.2056
>> 913.208.3600
>> 913.829.8690
>>
>> www.poolefire.com <http://www.poolefire.com/> Office Map 
>> <http://www.mapquest.com/maps/map.adp?address=19910%20W%20161st%20St&;
>> c
>> ity=Olathe&state=KS&zipcode=66062-2700&country=US&title=%3cb%3e19910%
>> 2 
>> 0W%20161st%20St%3c/b%3e%3cbr%20/%3e%20Olathe,%20KS%2066062-2700,%20%2
>> 0
>> US&cid=lfmaplink2&name=>
>>
>> This e-mail, and any files transmitted with it, are confidential and
>>     
> intended solely for the use of the individual or entity to which they 
> are addressed.  If you have received this e-mail in error, please 
> notify [EMAIL PROTECTED]
>   
>>  
>>
>>   
>> ---------------------------------------------------------------------
>> -
>> --
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>   
>> ---------------------------------------------------------------------
>> -
>> --
>>
>> No virus found in this incoming message.
>> Checked by AVG Free Edition.
>> Version: 7.5.446 / Virus Database: 268.18.8/714 - Release Date: 
>> 3/8/2007 10:58 AM
>>   
>>     
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
>   

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to