Kathryn,

That head can be 7-6 off the wall. The limiting factor is the maximum
allowable square footage per head. So if a head is 9-0 off one wall and 7-6
off the opposite wall the total allowable distance between heads in the
perpendicular direction would be A=SxL or L=A/S or
L=225/16-6 or L=13-6. Since the maximum that this head can be off a wall in
this direction is 7-6 that limits the opposite direction to 6-0. Since these
are maximums any configuration that doesn't exceed these limitations is
acceptable.

On 3/13/07, Kathryn Tyler <[EMAIL PROTECTED]> wrote:
> Although, speaking of the spacing within a small room... This has been 
> as issue of debate between 'designers' or layout fire protection 
> people for quite some time.
> To play the devil's advocate here; if you are allowed to move one head 
> 1-1/2 ft to making it 9 foot off the wall and you are allowed to go 15 
> foot to the next head and that head is allowed to be a max. of 6 foot 
> off the wall (because 15' - 9' = 6'), isn't the head that is 6' off 
> the wall still covering 7'-6" in the opposite direction.  225 sq. ft. 
> divided by 18' = 12'-6" not 12'-0", so why the 6'-0" ruling?
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Kathy 
> Tyler
> Sent: Tuesday, March 13, 2007 2:38 PM
> To: [email protected]
> Subject: RE: Small Room Rule
>
> Sorry I was referencing the square footage figured when you perform 
> hydraulic calculations and the demand for the square footage that is 
> required.
>
> Kathryn A. Tyler NICET IV, ASCET Member fire protection designer 
> Kelly-Wright & Associates PC Hvac, Plumbing & Fire Protection
> (520) 887-1919 ext. 302
> fax: (520) 696-0280
> [EMAIL PROTECTED] <blocked::mailto:[EMAIL PROTECTED]>
> www.kwmech.com <blocked::http://www.kwmech.com/>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>


--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to