> Subject: Re: Small Room Rule
> 
> Kathryn,
> 
> That head can be 7-6 off the wall. The limiting factor is the maximum
> allowable square footage per head. So if a head is 9-0 off one wall
> and 7-6 off the opposite wall the total allowable distance between
> heads in the perpendicular direction would be A=SxL or L=A/S or
> L=225/16-6 or L=13-6. Since the maximum that this head can be off a
> wall in this direction is 7-6 that limits the opposite direction to
> 6-0. Since these are maximums any configuration that doesn't exceed
> these limitations is acceptable.
> 
> On 3/13/07, Kathryn Tyler <[EMAIL PROTECTED]> wrote:
> > Although, speaking of the spacing within a small room... This has been as
> > issue of debate between 'designers' or layout fire protection people for
> > quite some time.
> > To play the devil's advocate here; if you are allowed to move one head 1-1/2
> > ft to making it 9 foot off the wall and you are allowed to go 15 foot to the
> > next head and that head is allowed to be a max. of 6 foot off the wall
> > (because 15' - 9' = 6'), isn't the head that is 6' off the wall still
> > covering 7'-6" in the opposite direction.  225 sq. ft. divided by 18' =
> > 12'-6" not 12'-0", so why the 6'-0" ruling?
> >
> > -----Original Message-----
> > From: [EMAIL PROTECTED]
> > [mailto:[EMAIL PROTECTED] On Behalf Of Kathy Tyler
> > Sent: Tuesday, March 13, 2007 2:38 PM
> > To: [email protected]
> > Subject: RE: Small Room Rule
> >
> > Sorry I was referencing the square footage figured when you perform
> > hydraulic calculations and the demand for the square footage that is
> > required.
> >
> > Kathryn A. Tyler NICET IV, ASCET Member
> > fire protection designer
> > Kelly-Wright & Associates PC
> > Hvac, Plumbing & Fire Protection
> > (520) 887-1919 ext. 302
> > fax: (520) 696-0280
> > [EMAIL PROTECTED] <blocked::mailto:[EMAIL PROTECTED]>
> > www.kwmech.com <blocked::http://www.kwmech.com/>
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> 
> 
> --
> Ron Greenman
> at home....
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> --
> No virus found in this incoming message.
> Checked by AVG Free Edition.
> Version: 7.5.446 / Virus Database: 268.18.11/721 - Release Date: 3/13/2007 
> 4:51
> PM
> 

-- 
No virus found in this outgoing message.
Checked by AVG Free Edition.
Version: 7.5.446 / Virus Database: 268.18.11/721 - Release Date: 3/13/2007 4:51 
PM
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to