10% is what we go by, based on your numbers your only at around 2% :(
Regards,
Brian Harris
First Defense Fire Protection
Design Engineer
[EMAIL PROTECTED]
704.948.3506 phone
704.948.3507 fax
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Charles
Thurston
Sent: Friday, March 16, 2007 10:19 AM
To: [email protected]
Subject: Mininum Supply Pressure
Hello All,
Let me be the one to start things today.
What is the minimum safety pressure allowed ? I have looked in 13 and
did not find it.... I have a situation where the safety pressure is
0.913 psi.
Basis is:
Hose 250
Static 67.00
Residual 38.00 @ 920.00
Available 40.128 @ demand of 882.87
Requires 39.215 psi
Leaving a safety of 0.913 psi
--
Best regards,
Charles mailto:[EMAIL PROTECTED]
Coastal Fire Protection