We stick with the 10% due to the fact that major insurance underwriters
(including FM & IRI) require 10% safety margins.

           Regards,
              Brian Harris
First Defense Fire Protection
        Design Engineer
   [EMAIL PROTECTED]
           704.948.3506 phone
           704.948.3507 fax

 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul Pinigis
Sent: Friday, March 16, 2007 9:31 AM
To: [email protected]
Subject: RE: Minimum Supply Pressure

If you can achieve 10% without spending your client's money (or your
own) great, but it is not necessary.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Friday, March 16, 2007 9:29 AM
To: [email protected]
Subject: RE: Minimum Supply Pressure

10% is what we go by, based on your numbers your only at around 2% :(

           Regards,
              Brian Harris
First Defense Fire Protection
        Design Engineer
   [EMAIL PROTECTED]
           704.948.3506 phone
           704.948.3507 fax

 
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Charles
Thurston
Sent: Friday, March 16, 2007 10:19 AM
To: [email protected]
Subject: Mininum Supply Pressure

Hello All,

Let me be the one to start things today.

What is the minimum safety pressure allowed ? I have looked in 13 and
did not find it....  I have a situation where the safety pressure is
0.913 psi.

Basis is:
 Hose 250
 Static 67.00
 Residual 38.00 @ 920.00
 Available 40.128 @ demand of 882.87
 Requires 39.215 psi
 Leaving a safety of 0.913 psi
 

-- 
Best regards,
 Charles                          mailto:[EMAIL PROTECTED]
Coastal Fire Protection

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to