The only numbers I have seen was from an Australian study over a 15
or 20 year review. It indicated around 60% (I think) was for 1
sprinkler and 80 something % (lets say 83%) for 3 sprinklers or
less. The interesting thing was that it was an AVERAGE for all
fires. That average is meaningless for higher challenge facilities
such as a warehouse.
Nonetheless, NFPA 13 doesn't care if you design TO the curve. It
ASSUMES that all those unknown variables about the water supply are
known (including degradation due to FUTURE growth). IT also assumes
that the system goes in EXACTLY as drawn). I always point to section
14.1.2 (02 ed) which says Deviation from approved plans shall require
permission of the AHJ. If someone wants to design to the curve or
close to it and the inspector sees a single elbow that isn't on the
plans, acceptance testing is terminated, news plans must be submitted
(and who says those plans are suppose to be immediately reviewed
since your screw up doesn't constitute an emergency for others), and
an inspection schedule.
Regardless of whether inherent safety factors exist, the methodology
is quite explicit on this matter and casually bumping up against the
curve is not a prudent path to follow.
Roland
PS: I haven't heard anyone argue that the hose demand is an
extraneous block of water providing a big cushion.
On Mar 16, 2007, at 7:01 AM, Paul Pinigis wrote:
My point is that there are already so many factors of safety built
into
the design of a system that one more is overkill upon overkill.
95% of
fires are controlled with one sprinkler operating, 98% of fires are
controlled with five or less operating, yet we calculate 1,500 square
feet (or 3,000 square feet for military projects), them we
overestimate
the friction loss in pipe and fittings, underestimate the water
supply,
them worry about adding an additional cushion.
Please, no "what about the other 2%" comments.
Paul J. Pinigis, P.E.
Chief Life Safety Engineer
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George
Church
Sent: Friday, March 16, 2007 9:56 AM
To: [email protected]
Subject: RE: Minimum Supply Pressure
Well, there ARE a few more considerations.
Was the supply adjusted for lowest tank gradient?
What confidence level do you have in the accuracy of the test data ?
What confidence level do you have that NO additional 90's will be
added?
What is the Owner's tolerance for risk?
NFPA #13 does NOT require a cushion. Good trade practice,
flexibility of
installation changes, common sense, and protection of your boss's
retirement
assets require a cushion of some sort. So may the various AHJs you
face-
water co, fire and code officials, insurance carrier, etc.
So you could be right and fine with .0001 cushion- but in so doing,
you
may
find yourself in a box scratching for 2.7 PSi in a .0001 margin when a
duct
doesn't go in as planned, some cable bracing is discovered, ANYTHING.
We deal with a water company that applies a .8 coefficient to all
hydrant
test. If your test was from a .7 hydrant, the supply is overstated and
your
system, upon correction, would be 5 or 6 PSI shy. Or if the tank level
was
3' above lowest tank gradient, your system won't work in August.
Or 4 heads could control the fire and everyone smiles. We just don't
know
EVERYTHING and we can't look into the future. I have trouble sleeping
when
we don't have 10%, and prefer 15 PSI+ on prelims on bid day. We just
analyzed a new site for a customer wanting to use K25s without a pump-
would
you tell him, based on 3.6 PSI cushion and ignorant of bar joist
spacing,
that it would? We're proceeding with a pump, and if things turn out
better
we can omit it, give him a credit for the pump, take some back with
the
$^
of k25's, but at least the money's in the job to start with.
When I was assetless and worked for others, I'd consider installing
what
you
have. Now, not without everyone involved knowing it, and not if I
was on
the
hook for the pump or larger piping replacement, or dual feed mains, or
whatever was needed to fix whatever changed and bumped us up. Imagine
going
to an owner with a $50,000 adder and explaining it with "we had to
add a
6"
90 at the top of the riser." Not a situation I'd look forward to !
glc
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Friday, March 16, 2007 9:31 AM
To: [email protected]
Subject: RE: Minimum Supply Pressure
If you can achieve 10% without spending your client's money (or your
own) great, but it is not necessary.
Paul J. Pinigis, P.E.
Chief Life Safety Engineer
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Friday, March 16, 2007 9:29 AM
To: [email protected]
Subject: RE: Minimum Supply Pressure
10% is what we go by, based on your numbers your only at around 2% :(
Regards,
Brian Harris
First Defense Fire Protection
Design Engineer
[EMAIL PROTECTED]
704.948.3506 phone
704.948.3507 fax
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Charles
Thurston
Sent: Friday, March 16, 2007 10:19 AM
To: [email protected]
Subject: Mininum Supply Pressure
Hello All,
Let me be the one to start things today.
What is the minimum safety pressure allowed ? I have looked in 13 and
did not find it.... I have a situation where the safety pressure is
0.913 psi.
Basis is:
Hose 250
Static 67.00
Residual 38.00 @ 920.00
Available 40.128 @ demand of 882.87
Requires 39.215 psi
Leaving a safety of 0.913 psi
--
Best regards,
Charles mailto:[EMAIL PROTECTED]
Coastal Fire Protection
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum