Todd,
In MA we can use 2 head design in a 3 decker now and have been.

http://www.mass.gov/Eeops/docs/dps/BuildingCode/780009.pdf

Tom

Owen,

I was at a seminar this week where they said that the MA Building 
Code might allow 13D systems in some 3 unit buildings in the next 
revision cycle. It's in the proposal and comment phase and nothing is 
cast in stone. There are a lot of 3 deckers out in this part of the 
world, but here the FDCs would be every 75 feet

Todd.


At 11:23 AM 3/17/2007, you wrote:
>Hello,
>
>How many cities out there allow the 3 unit condo complex to have 13D 
>system in each unit. Meaning, each unit has its own 1" meter, riser, 
>and two head calculation? The middle unit has two hour walls from 
>foundation up through the attic but without the parapet. Redondo 
>Beach has hundreds of these kind of lots. Since 1991 this 
>arrangement has been allowed. If other cities have these kind of 
>buildings but don't allow the 13D how are they protected, 13R?  If 
>Redondo did 13R they would have an FDC every 50' down many streets. 
>What is reasonable?
>
>Regards,
>Owen Evans
>(former plan checker of 7 years, back on the rescue to finish 25 
>years (thank God) )