Todd,
You will have to judge whether this would be analogous, but I would look
into FM Data sheet 2-2 Installation Rules For Suppression Mode Automatic
Sprinklers, and see if one of their design schemes for Mezzanines, Walkways,
or Conveyors might make some sense in your application.
Jeff Hewitt, PE, SET, SFPE (Prof. Member)
Corporate Engineer
Bi-State Fire Protection Corporation
636-946-0011
636-946-5172 (FAX)
This e-mail and any attachments are CONFIDENTIAL and may be protected by one
or more legal privileges. It is intended solely for the use of the
addressee identified above. If you are not the intended recipient, any use,
disclosure, copying or distribution of this e-mail is unauthorized. If you
received this e-mail in error, please notify the sender immediately at the
above captioned address.
----- Original Message -----
From: "Todd Williams - work" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Monday, March 19, 2007 7:34 AM
Subject: protecting ESFR
I'm working on a project in an ESFR warehouse where additional sprinklers
need to be provided beneath a duct. The duct is about 8-9 feet off the
floor in the 20 ft warehouse. My plan is to install 3 ESFR sprinklers
below the duct. The question I have is about protection of the sprinkler
and obstructions. I'm assuming that installing a sprinkler guard per 6.2.8
(2002) in not allowed. What other options are out there? This space is
occupied by some palletized storage and forklift parking, so damage is a
possibility. My original thought was upright ESFRs on sprigs, but that may
not work in this case. Thoughts?
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com