Ron - I have never seen a head below the fuel tank of a fire pump. Sorry, I know that does not help much.
Garth a fitter ----- Original Message ----- From: "Fletcher, Ron" <[EMAIL PROTECTED]> To: <[email protected]> Sent: Monday, March 26, 2007 1:10 PM Subject: Diesel pump fuel tank protection - IFC 3404.2.7.7 A local AHJ is requiring a sprinkler head under a diesel fuel tank in fully sprinklered fire pump room. >From the AHJ - "IFC 3404.2.7.7 Design of supports requires compliance with NFPA #30. NFPA 30-2003, 4.3.1.3: requires that steel support structures for tanks storing Class I, Class II, or Class III liquids be protected by materials having a fire resistance rating of not less than 2-hours." The intent of IFC 3404.2.7.7 is to require protection of the tank supports regardless of capacity. NFPA #30, 4.1.1 This chapter shall apply to the following: 4.1.1(2) "The storage of flammable and combustible liquids in portable tanks and bulk containers whose capacity exceeds 3000 L (793 gal)..." AHJ contends that 4.1.1 and 4..1.(2) are not applicable because the IFC is referencing the tank supports and does not specify a minimum size. Has any one else run into the requirement for a sprinkler under the fuel tank in a fully sprinklered pump room and what did you fight or comply. Does anyone know of interpretations or commentary regarding tank supports. Ron Fletcher Aero Automatic Phoenix, AZ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum