Technically by the wording in NFPA 13, No.  But from a realistic
standpoint, maybe.  If it's just a walkway with no chance of storage
below it and the discharge from the overhead sprinklers can reach the
area below the walkway without any interference, then probably not.
But sometimes you have to look at the space and make a judgment call
beyond what it written in black and white.


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Eric
Shelton
Sent: Thursday, April 05, 2007 1:30 PM
To: [email protected]
Subject: RE: open grate flooring

If a floor is less than 48" wide but is adjacent to a wall, does it need
sprinklers under it?

/Eric Shelton
Hankins and Anderson, Inc.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Thursday, April 05, 2007 1:27 PM
To: [email protected]
Subject: RE: open grate flooring

Just because the floor is open grating doesn't discount the need of
sprinklers below it.  Grating can still create an obstruction to
sprinkler discharge.


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Rod
DiBona
Sent: Thursday, April 05, 2007 1:07 PM
To: [email protected]
Subject: open grate flooring

I am working on a large jail project where the architect has asked me to
provide value engineering ideas. One of the things that I am considering
bringing to his attention is the possibility of turning their upper cell
walkway into an open grate flooring of 4' or less. I was pretty sure
that this would eliminate the need for sprinklers under these walkways
but I wanted to substantiate it before I presented it. NFPA 13 02
edition 8.5.5.3.1 states " Sprinklers shall be installed under fixed
obstructions over 4ft wide such as ducts, decks, open grate flooring,
cutting tables, and overhead doors". Am I correct in assuming that if
these "floors" are 4' or less that sprinks will  not be required? I
thought that I remembered that there were other requirements such as
percentage or size of openings similiar to the meshing in nursing home
curtains but I can't find it anywhere. Any help is appreciated.
 
Thanks,
 
Rod DiBona
Rapid Fire Protection
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to