You may want to do a little more digging into how the whole system
works. Both polyester and epoxy resins are flammable liquids (at
least the ones in my garage are). If there is a spraying or flow
coating operation, the hazard could go to EH2. Also, depending on
what kind of boats, you may have large cabins which could create a
shielded fire issue. Be aware of raw material storage and
distribution as well. The fumes from this type of operation are not
only flammable, but produce a serious health hazard, so there may be
an exhaust system that could require duct sprinklers. There's a lot
to think about.
At 03:35 PM 4/9/2007, you wrote:
Would this be classified as OH II (resin application)?
Thanks,
Dewayne
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com