Dewayne,

I imagine there are some FD guys out there that will know for sure but I
would believe that you would not include any pressure from the city water.
I believe the FD would not want to pressurize the system beyond 150 PSI not
knowing if the system components could take pressure beyond 175 since that
is what most are rated.

Cliff
Fire Design, Inc.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: Tuesday, April 10, 2007 10:23 AM
To: SprinklerFORUM
Subject: Manual wet standpipes

We have a discussion in our office on the correct way to calculate a
manual wet standpipe.
Our local fire department pumper trucks are set for 150PSI @ 1500 GPM
and contain a 1500 gallon tank  For calculating a manual wet standpipe
back to the fire department connection, should we only use the rated
capacity of the pumper truck or are we allowed to add in the city water
pressure/flow available at the hydrant at which they hook up to?  IE:
Either treat it as a stand alone fire pump off a tank or as a standard
fire pump w/ city water supply added in.   
Thanks,
Dewayne
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)