If George can't do it, I have a friend who is likely a member and may help out.
At 06:27 PM 4/25/2007, you wrote:
That's why you gotta keep your tongue IN YOUR CHEEK or risk shorting out the
keyboard. And my keyboard is centered between a couple QR concealed
sprinklers.....just in case.
Hey- let's go back to getting the NAHB in check. Strangely enough, I think
we just joined an affiliate of NAHB (to save $23,000/yr on our health
insurance) so I'll check with my boss and see if it included website access
of NAHB's site. If so, I'll download and help them spread their message- to
their foes.
glc
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, April 25, 2007 4:54 PM
To: [email protected]
Subject: RE: 1/2" thread - 8 K sprinklers
I usually use my fingers for typing, George's way seems like it would
make the keyboard all wet..........
Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC 29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George
Church
Sent: Wednesday, April 25, 2007 4:40 PM
To: [email protected]
Subject: RE: 1/2" thread - 8 K sprinklers
I trust y'all understand I type tongue in cheek, and this was intended
to be an opening of discussion with the AHJ.
I'd hope he'd be glad you spotted the impact and are correcting the
unforeseen losses. Not everyone would.
glc
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John
Drucker
Sent: Wednesday, April 25, 2007 2:44 PM
To: [email protected]
Subject: RE: 1/2" thread - 8 K sprinklers
Exactly correct.
John Drucker
Fire Protection Subcode Official (AHJ)
Red Bank, NJ
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Wednesday, April 25, 2007 1:14 PM
To: [email protected]
Subject: Re: 1/2" thread - 8 K sprinklers
George is practicing skating on some mighty thin ice. The problem would
be that it isn't an existing system until AFTER it is accepted.
This requirement has been in the standard a long time so whatever the
basis, it is lost as ancient history. A reasonable assumption (since it
is allowed for existing systems, thus must still work) is that the
1/2 NPT unnecessary restricts the flexibility of a system that already
has a higher flow demand than typically provided by K 5.6.
Roland
On Apr 25, 2007, at 9:38 AM, George Church wrote:
> I wouldn't see the harm in asking.
> You could also go inand install the k5.6 heads, re-run the calcs, and
> then retro the 1/2 K8 heads in accordance with the code into what is
> now an "existing" system.
> glc
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Greg
> McGahan
> Sent: Wednesday, April 25, 2007 12:20 PM
> To: [email protected]
> Subject: 1/2" thread - 8 K sprinklers
>
> NFPA 13 clearly states that we can not use 8.0 k heads with 1/2"
> threads in
> new installations. I assume there are reasons for this but I do not
> know them.
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com