Todd, I think what that means is that the minimum distance from a column is never required to be more than 24 in. For example, if the column is 10" x 10", then the minimum distance is 24" instead of 3x10 = 30".
Tony Liddic, CET AEC Fire & Security 400 Fame Rd. West Carrollton, OH 45449 937-866-4158 937-865-0212 fax [EMAIL PROTECTED] -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams - work Sent: Thursday, May 10, 2007 1:13 PM To: [email protected] Subject: column obstruction Section 8.6.5.2.1.3 details how to handle a column obstruction. The 3x minimum dimension makes sense, but I don't quite get the "maximum clear distance required shall be 24 in". Unless there is a column protection issue, why is there a maximum that a sprinkler can be from a column? Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut 860-535-2080 www.fpdc.com _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) No virus found in this incoming message. Checked by AVG Free Edition. Version: 7.5.467 / Virus Database: 269.6.6/795 - Release Date: 5/9/2007 3:07 PM No virus found in this outgoing message. Checked by AVG Free Edition. Version: 7.5.467 / Virus Database: 269.6.6/795 - Release Date: 5/9/2007 3:07 PM _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)