The actual sprinkler operation time is a function of the fire size and growth because the heat transfer to the element is related to the temperature and velocity of gasses passing the link/bulb, plus other factors. I use a program to calculate the difference in time, there are several available that will work. FDS if you use it, otherwise if you go to the appendix in NFPA 72 there are manual calculation methods shown. The problem you will have is getting the actual response time from the manufacturer, otherwise you have to use the classification numbers.

I also have a circulating hot air test oven that I use to test the actual response time of a particular sprinkler. It is similar to the UL plunge test .

Michael

At 09:06 AM 5/14/2007, you wrote:
We have a customer, a VA Hospital, that is trying to justify changing from
Standard response to quick response sprinklers.  We have discussed the RTI
and other factors that make the QR's respond faster, but he is asking if we
know of any time differences that are verifiable.  What he needs is some
idea that QR's respond in X seconds and Standard response respond in Y
seconds to show the difference.  I have looked in the sprinkler handbooks
( 1999 to 2007) and the Fire Protection Handbook, but only find references
to RTI, no actual times.  The FM standard lists 1:15 as the time for QR, but
I could not find standard response.
   Any help is appreciated.

Joseph C. Stough CET, CFPS
Tilley Fire Equipment Co.
Tel. 215-345-8066 X22
Fax: 215-345-9357
[EMAIL PROTECTED]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


__________ NOD32 2264 (20070514) Information __________

This message was checked by NOD32 antivirus system.
http://www.eset.com

Michael M. Fitz, P.E., C.F.I.
MDE Inc.
700 South Industrial Way
Seattle, WA  98108
Main 206-622-2007
Direct 206-957-2140
Fax 206-622-2248
Home Office 360-427-2751
Cell 206-321-1804
www.mde.com _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to