I've dealt with these things before and the problem is there is no space
to put a sprinkler anywhere within the pocket.  Just not physically
possible.  The track fills the top of the pocket and the space beside
the curtain is minimal at best (usually inches).  If you were to do
anything it would be to come into the space from the side and spray
downward with a pattern similar to a window or cornice style sprinkler.
And that's based on there being ANY access from the sides which in most
cases, there is none.  Whether the 55sf rule can be applied is
questionable.  Since the space is not ABOVE any room but actually within
the occupied space and OPEN to the occupied space it doesn't appear to
be applicable.  

The better option would be to establish the flame/smoke rating for the
curtains, establish that the pocket area is constructed completely of
non-combustible materials and than make a case for the application where
conditions are similar to either 8.14.1.2.10 or 8.14.1.2.12. (2002 ed.
as referenced) Whether the "combustible" component within the space is a
curtain or insulation shouldn't make that much difference if the curtain
can meet the same requirements as the insulation.  


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Tom
Sent: Tuesday, May 29, 2007 3:44 PM
To: [email protected]
Subject: Re: RE: folding door alcove

If the space is more than 55 sq.ft you could possibly put an upright
head above the ceiling track?
Tom Berry
Precision Fire Protection Inc

From: "A.P.Silva" <[EMAIL PROTECTED]>
Date: 2007/05/28 Mon PM 12:01:10 CDT
To: [email protected]
Subject: RE: folding door alcove

I design with concealed sprinklers in such pockets. If the contractor
feels it is not required, I let him negotiate with the AHJ.

NFPA always had a section that permits deletion of heads in a concealed
space above an isolated small room not exceeding 55 sq.ft. (NFPA 13,
2002,
8.14.1.2.9) I have never come across a situation where it could be
applied.
But many times the folding partition pockets and similar linen closets.
Could it be this section would apply?

Just thinking.

Tony   

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams
- work
Sent: May 28, 2007 6:34 AM
To: [email protected]
Subject: folding door alcove

A question came up on a hotel with a meeting room that could be divided
in two by a folding partition. The partition folds into a space roughly
the size of a closet. The ceiling of this space is mostly track that
partition runs on. Does this space need to be sprinklered? If so, does
anyone have any good ideas how to do it?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to