why not ensure there are 2 sprinklers
close enough to the alcove opening
(at ceiling level) and
make the case that they will get and
wet any fire that comes running out of there?

A sprinkler on either side (with minimum 6 ft
separation would take care of the case where
the door was extended out of the alcove.

Sounds like oxygen is going to be a problem
for this fire to keep on burning, if the space is
as tight as you are saying...although if there
is enough oxygen, wall fires grow FAST...
especially plastic wall fires.

scot deal
excelsior fire




On 5/29/07, [EMAIL PROTECTED] <[EMAIL PROTECTED]> wrote:

I've dealt with these things before and the problem is there is no space
to put a sprinkler anywhere within the pocket.  Just not physically
possible.  The track fills the top of the pocket and the space beside
the curtain is minimal at best (usually inches).  If you were to do
anything it