Hello George,

The AHJ is suggesting we reuse the heads to save cost while I bid the
job with replacing all the heads.

Monday, July 2, 2007, 1:07:06 PM, you wrote:

> Only new heads shall be used.

> I'm not looking it up, but I doubt there's much reading between the lines on
> this one. Despite that, a friend who's on #13 told me (and maybe on the
> Forum, don't recall, hence he remains unnamed here) he knows better but
> cannot compete in his market if he didn't re-use them as you want to- and
> maybe (until a lawsuit) it's a local tradition sort of thing.

> In this case, it looks like the AHJ is enforcing the code, and I don't know
> where to find a leg to stand on that would hold up to the inevitable
> question "what didn't you understand about only new heads shall be used?".

> glc

> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Charles
> Thurston
> Sent: Monday, July 02, 2007 12:36 PM
> To: [email protected]
> Subject: Remodel Jobs

> Hello sprinklerforum,

>   Minor debate with an AHJ over reusing heads in a space that is
>   remodeling. 6.2.1 Will only allow new heads to be installed. I know
>   about removing the head reducer from the pipe and putting back on a
>   new pipe to move a head, But these are 401 style and the reducer is
>   covered by the cup. IS there anything in NFPA13 to allow reuse of
>   heads when a space is remodeled ?




-- 
Best regards,
 Charles                            mailto:[EMAIL PROTECTED]