True unless the dwelling units meet the compartment criteria of
6.6.7.1.3. Then QR can be substituted for residential and then dry can
be used. Again think 3 or 4 heads max in the typical hotel/motel room
(dwelling unit/compartment).

On 7/4/07, Todd Williams - work <[EMAIL PROTECTED]> wrote:
Since there aren't any residential sprinklers listed for use on a dry
system, 5.3.2 (2) becomes moot. That was my assumption.


At 11:04 AM 7/4/2007, you wrote:
>Todd,
>
>A dry system would not be a reason to cause the system to become 13.
>See 13R, 2002, 5.3.2. A dry pipe system is acceptable. It's CPVC that
>is not listed for dry system use. 5.3.3 says to install dry pipe
>systems in accordance with 13 but not that a dry pipe system makes it
>a 13 system. I read this to mean that all rules, including coverage,
>are still dictated by 13R but because it is silent on low points,
>slope, compressor fill times, etc. that 13 applies in that regard.
>
>As for anti-freeze glcerin is required in the described suituation
>because it's the only acceptable type listed for CPVC.  If the system
>was not plastic propylene glycol would be acceptable.
>
>If this is not a stand alone system then anti-freeze in the UG would
>be unacceptable. On the other hand if it is fire protection only then
>an RPBA/RPDA should be acceptable protection from the public/private
>point of attachment which is typically the property line.
>
>Another comment for Charles. If you put a "RPZ" device in this system
>in a vault the vault needs a drain that can handle the maximum
>discharge rate of the device and be able to drain run-off that gets
>into it. The discharge port of the device cannot be under water.
>
>On 7/4/07, Todd Williams - work <[EMAIL PROTECTED]> wrote:
>>Where did these 'requirements' come from? It sounds to me that the
>>owner needs to have an Engineer come in and work with him (or her) on
>>a system design.
>>
>>I believe that with the anti-freeze that it could still be a 13R
>>system. A dry system would push it to 13. The water company would
>>probably have something to say about glycerine (remember, no glycol
>>in CPVC) in underground mains. Since the existing system is dry and
>>(I assume) a 13, is there going to be an issue decreasing the
>>protection level to 13R? The AHJ or Insurance Comapny may weigh in on that.
>>
>>Without knowing the type and arrangement of the building, It's
>>difficult to make any comments about the impact of the soffits. I'm
>>not sure I follow Ron's train of thought.
>>
>>Since you spoke about outside walkways, is part of this system
>>outside? If so, then galvanized pipe and fittings plus wax coated
>>sprinklers on a dry system would be appropriate.
>>
>>
>>At 09:43 PM 7/3/2007, you wrote:
>> >Hello sprinklerforum,
>> >
>> >         I am open to suggestions on this one.
>> >
>> >         We have a customer in a 4 story residential building
>> > wanting to replace the entire system due to rusted/leaking pipes in
>> > the old system.
>> >
>> >         They are requiring the system to be installed with CPVC piping.
>> >
>> >         They are requiring the ENTIRE system to be filled with
>> > Anti-Freeze including the underground.
>> >
>> >         They are wanting to put the DCDA Backflow, Then the Alarm
>> > Valve, Then the RPZ Backflow and Expansion Tank into a hotbox outside.
>> >
>> >         To me it looks like the use of Anti-Freeze bumps it to a 13
>> > system instead of 13R. The new piping is to be built into new
>> > soffits on the outside of the building walkways. They have a Dry
>> > Pipe system now and do not want the leaking problems they have now
>> > to recur in a few years like the existing 10 year old system. I am
>> > not even bring up the subject of Anti-Freeze recovery/reuse when
>> > the system is tested or when the Alarm company does a flow to test
>> > the WF switches quarterly. The Main Drain flow test is another subject...
>> >
>> >--
>> >Best regards,
>> >Charles Thurston
>> >Coastal Fire
>> Protection                          mailto:[EMAIL PROTECTED]
>> >
>> >
>> >_______________________________________________
>> >Sprinklerforum mailing list
>> >[email protected]
>> >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >
>> >To Unsubscribe, send an email to:[EMAIL PROTECTED]
>> >(Put the word unsubscribe in the subject field)
>>
>>Todd G. Williams, PE
>>Fire Protection Design/Consulting
>>Stonington, Connecticut
>>860-535-2080
>>www.fpdc.com
>>
>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>>To Unsubscribe, send an email to:[EMAIL PROTECTED]
>>(Put the word unsubscribe in the subject field)
>
>
>--
>Ron Greenman
>at home....
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>To Unsubscribe, send an email to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to