Car Wash is classified use group B. (IBC 304). The sprinkler threshold for B occupancies is relatively high, must be a large carwash.
But assuming this is a sprinklered property, and since its an NFPA-13 system, life safety and property protection are objectives. Lets look at this smartly. If theres a fire under this roof attached to a building can the fire spread into the attached structure, or is there a fire separation/barrier ?. John Drucker Fire Protection Subcode Official (AHJ) New Jersey -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of George Church Sent: Monday, July 09, 2007 3:41 PM To: [email protected] Subject: RE: hand car wash Ask the AHJ whose opinion is what matters, not yours or mine, does washing a car constitute "storage" and the resultant sprinkler requirement. Much as it pains me, Thom's right. glc -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon Sent: Monday, July 09, 2007 3:24 PM To: [email protected] Subject: Re: hand car wash Non-combustible Porte chiere's don't require protection, Non-combustible projections and covered walkways not used for storage don't require protection, seems like a visit with the AHJ could resolve the fact that its "attached", and falls somewhere in between those two. Thom McMahon Firetech, Inc. 2560 Copper Ridge Dr Steamboat Springs, CO 80488-2136 Tel: 970-879-7952 Fax: 970-879-7926 ----- Original Message ----- From: "Greg McGahan" <[EMAIL PROTECTED]> To: <[email protected]> Sent: Monday, July 09, 2007 1:14 PM Subject: hand car wash Situation: Non combustible overhang with nothing underneath it. It will only be used to hand wash cars. 2 questions: Protection required? What hazard? Greg Living Water Fire Protection, LLC 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 Fax: 850-937-1852 the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)