The FDC is supposed to be connected to the system side of the fire pump, in which case the bypass would be irrelevant.

Richard L. Mote
Designer
Rowe Sprinkler Systems, Inc


----- Original Message ----- From: "John Drucker" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Wednesday, July 11, 2007 2:08 PM
Subject: RE: impairment procedures


Roland, et. al.

Dave Phelan pretty much summed up the issues surrounding fire watches.
There is no one size fits all. The determination as to when it is
appropriate to employ a fire watch requires a through evaluation of fire
protection objectives.

For example in a small building where life safety and only life safety
is the issue a fire watch may be employed to patrol, notify the fire
department and evacuate the building. The number of fire watch personnel
must be determined.  Not so long ago we had a fire pump burn up in a
high rise. There is no suitable fire watch for this scenario since
suppression is a significant component of life safety and not simply
detection and notification. The building owner had the choice of
evacuating the premises or having a fire department engine 24/7
pressurized on the FDC for the duration of the impairment. The latter
was chosen. (PS- One more reason why a bypass should always be
installed).

Fire Protection is like a jigsaw puzzle, take away too many and/or major
pieces and we loose sight of the big picture.

John Drucker
Fire Protection Subcode Official
Also an AHJ in NJ


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Wednesday, July 11, 2007 10:10 AM
To: [email protected]
Subject: Re: impairment procedures

You would be one tough AHJ.

I don't believe he would be required to shut down but would have to
implement an impairment procedure, part of which is a manned fire watch
24/7.  I am sure there are some occupancies that would entail
shutting down the operation, for instance high hazard occupancies,
high occupant facilities (aka The Station), etc.  I'll let our AHJ
friends chime in on the specifics.

Roland

On Jul 11, 2007, at 6:33 AM, Ken Holsopple wrote:

Rod,

One other thing that might be useful is asking the owner if he is
willing to shut his hotel down if the pool requires maintenance and
the pool has to be drained.


Best Regards,
Ken Holsopple
Design Manager
Rowe Sprinkler Systems, Inc.
570-837-7647


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:Sprinklerforum-
[EMAIL PROTECTED] (Put the word unsubscribe in the subject
field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to