If there is nothing on the building code side driving you to have a
sprinklered building, the protecting specific hazards is acceptable, but
you will still not have a sprinklered building.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, August 01, 2007 12:19 PM
To: [email protected]
Subject: RE: Interpretation of nfpa 13, 8.1.1(1)

We have met and satisfied all the requirements of the building code for
the installation.


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Wednesday, August 01, 2007 12:00 PM
To: [email protected]
Subject: RE: Interpretation of nfpa 13, 8.1.1(1)

Are there allowances for height, area, fire-endurance, etc. being
applied to the project based upon it being sprinklered?  If so, look at
those exceptions very carefully.

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, August 01, 2007 11:56 AM
To: [email protected]
Subject: Interpretation of nfpa 13, 8.1.1(1)

I've got a gypsum board mfg. facility.  Several areas are unsprinkled as
permitted by the IFB due to the lack of hazard present and building
separations.  I also have hazardous storage, paper storage and offices
which are sprinkled, again in accordance with the IFB and IFC.  The AHJ
is saying that if we sprinkler anything then EVERYTHING needs to be
sprinkled regardless of what the building code says based on 8.1.1(1).
"Sprinklers shall be installed throughout the premises."

Does anyone have a formal interpretation on this sentence?  

If he has his way I'd have to protect 500,000 sf of finished gypboard.  


Craig L. Prahl, CET


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to