Well thanks to those who replied. We just got a call from the AHJ and the ruling was changed. We're good to go.
Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.lg.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Paul Pinigis Sent: Wednesday, August 01, 2007 12:21 PM To: [email protected] Subject: RE: Interpretation of nfpa 13, 8.1.1(1) If there is nothing on the building code side driving you to have a sprinklered building, the protecting specific hazards is acceptable, but you will still not have a sprinklered building. Paul J. Pinigis, P.E. Chief Life Safety Engineer -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Wednesday, August 01, 2007 12:19 PM To: [email protected] Subject: RE: Interpretation of nfpa 13, 8.1.1(1) We have met and satisfied all the requirements of the building code for the installation. Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.lg.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Paul Pinigis Sent: Wednesday, August 01, 2007 12:00 PM To: [email protected] Subject: RE: Interpretation of nfpa 13, 8.1.1(1) Are there allowances for height, area, fire-endurance, etc. being applied to the project based upon it being sprinklered? If so, look at those exceptions very carefully. Paul J. Pinigis, P.E. Chief Life Safety Engineer -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Wednesday, August 01, 2007 11:56 AM To: [email protected] Subject: Interpretation of nfpa 13, 8.1.1(1) I've got a gypsum board mfg. facility. Several areas are unsprinkled as permitted by the IFB due to the lack of hazard present and building separations. I also have hazardous storage, paper storage and offices which are sprinkled, again in accordance with the IFB and IFC. The AHJ is saying that if we sprinkler anything then EVERYTHING needs to be sprinkled regardless of what the building code says based on 8.1.1(1). "Sprinklers shall be installed throughout the premises." Does anyone have a formal interpretation on this sentence? If he has his way I'd have to protect 500,000 sf of finished gypboard. Craig L. Prahl, CET _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)
