New spec warehouse designed for Ordinary Hazard Group II occupancy. Halfway
through construction we find out that half of the warehouse is leased to a
major retailer who also performs home improvements and they intend to store
home improvement items in the space. 

I thought we were correct in sending the GC an OIC and asking the tenant to
complete and return. It comes back with vinyl siding stored in racks to
11'-0".

We inform the owner and GC (one and the same) that the system is inadequate
and needs to be addressed. Mr Owner calls me, blesses me thoroughly for
trying to monitor the world and asks if I intend to do daily inspections of
the premises to make sure the tenant is storing in accordance with OH2 and
etc, etc, etc.

I review 13 4.3 and A4.3 and realize that there is a tremendous hole in the
standard. Although the intent is spelled out in the appendix it stops short
of describing the exact situation that we have here.

Why doesn't it say that the OIC must be reviewed and resigned by the owner
after the building is built? In this case the owner feels that if we have an
OIC prior to starting the job we should shut up and move since 13 does not
REQUIRE us to revisit the design after that. The change of occupancy does
not technically apply since the building has not yet, nor will be occupied
when we finish.

In order to cover us, we are going to write a letter stating that the system
is OH2 and any tenants should comply with all that entails or they are not
in compliance and the system is not adequate.

And before you all attack me and tell me to walk, this happens to be one of
the most stable and established GC's in our little town and we really do not
want to alienate him.

Still fuming,
Greg

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to