  Thanks for your answer,I am doing manual hydraulic calculations for carbon 
dioxide and Halon 1301 systems based on NFPA-12 and NFPA-12A easily but 
NFPA-2001 has not stated enough information to determine nozzles pressure and 
flow rate for a HCF-227ea System, just I can calculate the required mass of 
FM-200! I know that now a days UL listed computer softwares are able do to a 
complete hydraulic calculations, but actually these softwares are also based on 
some formulas and equations. The more I look for, the less I find! I would like 
to ask if it is possible to do hydraulic calculations of a engineered FM-200 
System manually? Or the formulas are secrets and only software owners like 
Hughes associates have it!? If NFPA has the formulas for hydraulic calculations 
of HCF-227ea Systems, why doesn't NFPA publish them?
Thanks for your kind help
  Regards,
Reza

"Ford, Charles" <[EMAIL PROTECTED]> wrote:
  Reza, There are many issues with your question and statements. NFPA 12A is 
[more accurately was] for
Halon 1301 ONLY. 
NFPA 2001 describes the calculation method for FM-200 although I'm not sure 
they can be duplicated by
normal people. We have all been disappointed by FM-200 Calcs but I see no other 
solution other than
the specific manufacturers UL listed computer program(s). 


Burton Ford
NICET IV Special Hazards, CFPS
Member AFAA
[EMAIL PROTECTED]
267-487-1000
Fax 267-487-1010

This e-mail transmission contains information that is intended to be 
confidential and privileged. If
you receive this e-mail and you are not a named addressee you are hereby 
notified that you are not
authorized to read, print, retain, copy or disseminate this communication 
without the consent of the
sender and that doing so is prohibited and may be unlawful. Please reply to the 
message immediately
by informing the sender that the message was misdirected. After replying, 
please delete and otherwise
erase it and any attachments from your computer system. Your assistance in 
correcting this error is
appreciated. Thank you. Cintas Corporation

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On
Behalf Of Reza Esmaeili
Sent: Wednesday, August 08, 2007 12:50 PM
To: [email protected]
Subject: A Question HFC-227ea System Hydraulic Calculation

Dear Friends,
I know this forum is not the proper place for asking this questions, but I am 
completely
disappointed on hydraulic calculation of a FM-200 system. I would be thankful 
if you can answer my
question or help me how th solve my problem. My question is as below:

To do hydraulic calculation of a FM-200 600Psi, system first I want to 
calculate the percent of
FM-200 in piping to be able to find out working pressure, there is a formula in 
NFPA 12A to determine
percent of agent in piping, which is k1/[(W/V)+ K2 ] but there is nothing about 
this issue in NFPA
2001, I want to know if I can calculate percent of HFC-227ea in piping based on 
the same formula which
is in NFPA 12 A, can I use the same K1 & K2 Constants of Halon 1301 for 
HFC-227ea? If not, how can I
calculate?
I don't know if I am going the right way, I was looking for a worked example 
but I couldn't find,
can anybody help me?
Thanks in advance.
Regards,
Reza



---------------------------------
Be a better Heartthrob. Get better relationship answers from someone who knows.
Yahoo! Answers - Check it out. 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



This e-mail transmission contains information that is intended to be 
confidential and privileged. If you receive this e-mail and you are not a named 
addressee you are hereby notified that you are not authorized to read, print, 
retain, copy or disseminate this communication without the consent of the 
sender and that doing so is prohibited and may be unlawful. Please reply to the 
message immediately by informing the sender that the message was misdirected. 
After replying, please delete and otherwise erase it and any attachments from 
your computer system. Your assistance in correcting this error is appreciated.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


       
---------------------------------
Be a better Globetrotter. Get better travel answers from someone who knows.
Yahoo! Answers - Check it out.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to