    I have a question about a sprinkler system, with the specifications below:

     
  - Main fire pump outlet pressure: 9 Bar.
   

    Most Remote Room Specifications:
- Number of sprinklers in the room: 140 Pcs

    - Required Density: 24.5 l/min/m©÷
  - Most remote sprinkler pressure loss: 2.5 to 3 Bar.

    - One sprinkler covarage: 9m©÷

     

    As the density is 24,5 l/min/m©÷ and (1spk /9m©÷) so flow rate of each 
sprinkler is 220.5 l/min=58.3 GPM 
    Q=K¡îP then  58.3 = K ¡îP

    If K=80 (or 5.55) then 58.3 = 5.55 ¡îP then P = 7.6 Bar

    If K=160 (or 11.1) then 58.3 =11.1 ¡îP then P = 1.9 Bar

     

    - If we choose K=80, as the pressure at most remote sprinkler is about 6 - 
6.5 Bar so the available pressure is less than the required sprinkler pressure 
which is 7.6 Bar.

    - If we choose K=160, we don't have pressure problem but the density will 
be more than what we require. GPM = 11.1 ¡î(6x14.51) = 104 GPM

     

    Can anyone kindly let me know what K factor should I choose and why?
  Thanks for your help,
  Reza



       
---------------------------------