the way to envision it is that you have to be able to cover the roof just like an occupied floor (excluded steeply pitch areas as identified in 14) so a single connection can NOT be used based on having 500 ft of hose. Fortunately, Rich guided us to explicit criteria.

To summarize, IF a stairwell has access to the roof, then the highest landing in that stairwell will suffice otherwise extend it to the roof as identified in the Annex.

Roland

On Aug 9, 2007, at 6:11 AM, Russell wrote:

The buildings in the area in which I live rarely, if ever, are more than three stories high, so my experience and knowledge of standpipes is limited to the contents of NFPA14 and that is the source of my question. I have a four story motel with two standpipes with a combined system. I must install
a roof manifold per code but I’m not sure if it should be one off each
standpipe. I would say yes because the standpipe pipe is sized by the
required hydraulic calculation procedure which utilizes both standpipes which share the required flow, so if there is only one roof manifold at the remote standpipe then the total flow could require larger pipe which in turn would make the initial calc procedure null and void. How many roof manifolds
should I install?



Any suggestions will be greatly appreciated,

Ron


Internal Virus Database is out-of-date.
Checked by AVG Free Edition.
Version: 7.5.467 / Virus Database: 269.8.13/843 - Release Date: 6/10/2007
1:39 PM

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:Sprinklerforum- [EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to