And just to confound the discussion, though I did indeed find the code
section, oddly enough here in Seattle, we have ammendeded that section
to only require one of the standpipes to have roof connections, unless
the roof size requires more than 200 ft. of hose distance from that
connection, in which case additional hose connections on the roof are
required.  We also changed the requirement to require the roof
connection to include two 2 ½ in. hose connections.

There are lot's of opinions as to the purpose of roof connections, very
little consensus on this issue in my experience.

Rich Richardson
Seattle Fire Department

>>> Roland Huggins <[EMAIL PROTECTED]> 08/09/07 9:36 AM >>>
PLEASE NOTE: Internet email sent to @ci.seattle.wa.us addresses will no
longer be accepted and delivered starting AUGUST 31, 2007 at Noon. 

This email was sent to your old @ci.seattle.wa.us email address.

IF THIS IS A VALID EMAIL FROM A REAL PERSON OR SOURCE:
1) If from a Person, please contact them and have them update your
email address from @ci.seattle.wa.us to @Seattle.Gov 

2) If this is an important newsletter or relayed email from a ListServ,
please either update your email address with that  service or start a
new subscription using your @Seattle.Gov email address.

IF THIS IS UNIMPORTANT OR JUNK EMAIL, please do nothing.  It will stop
being delivered after August 31, 2007

For more information, please contact your Service Desk.
============================================================

the way to envision it is that you have to be able to cover the roof  
just like an occupied floor (excluded steeply pitch areas as  
identified in 14) so a single connection can NOT be used based on  
having 500 ft of hose.  Fortunately, Rich guided us to explicit  
criteria.

To summarize, IF a stairwell has access to the roof, then the highest 

landing in that stairwell will suffice otherwise extend it to the  
roof as identified in the Annex.

Roland

On Aug 9, 2007, at 6:11 AM, Russell wrote:

> The buildings in the area in which I live rarely, if ever, are more 

> than
> three stories high, so my experience and knowledge of standpipes is 

> limited
> to the contents of NFPA14 and that is the source of my question. I  
> have a
> four story motel with two standpipes with a combined system. I must 

> install
> a roof manifold per code but I’m not sure if it should be one off
each
> standpipe. I would say yes because the standpipe pipe is sized by
the
> required hydraulic calculation procedure which utilizes both  
> standpipes
> which share the required flow, so if there is only one roof  
> manifold at the
> remote standpipe then the total flow could require larger pipe  
> which in turn
> would make the initial calc procedure null and void. How many roof  
> manifolds
> should I install?
>
>
>
> Any suggestions will be greatly appreciated,
>
> Ron
>
>
> Internal Virus Database is out-of-date.
> Checked by AVG Free Edition.
> Version: 7.5.467 / Virus Database: 269.8.13/843 - Release Date:  
> 6/10/2007
> 1:39 PM
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected] 
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
>
> To Unsubscribe, send an email to:Sprinklerforum- 
> [EMAIL PROTECTED] 
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected] 
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 

To Unsubscribe, send an email
to:[EMAIL PROTECTED] 
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to