Just as Gregg describes (full coverage above with pendants below) that is the 
requirements we use here.  I however, do believe this is addressed in NFPA13.  
Simple as providing coverage at the roof like always and providing heads under 
obstructions, similar to sprinklers under ducts.  The only point of discussion 
on the subject in my opinion, is exactly how many and how large can openings be 
in a concealed space before it is no longer considered a concealed space.

Rich Richardson
Seattle Fire Department

>>> "Gregg Fontes" <[EMAIL PROTECTED]> 08/15/07 11:36 AM >>>
In a similar project, the AHJ required full coverage above the clouds and
pendants at the clouds.  Since no specific code addressed this, the AHJ made
the final decision.  

For what it is worth,
Gregg Fontes
Cen-Cal Fire Systems, Inc.
(209)334-9119

-----Original Message-----
From: [EMAIL PROTECTED] 
[mailto:[EMAIL PROTECTED] On Behalf Of Rapid Fire -
Bismarck
Sent: Wednesday, August 15, 2007 11:22 AM
To: [email protected] 
Subject: Ceiling Clouds throughout Band / Choir Room

Scenario:
Band - Choir room(s) with 4' x 4' acoustical dampening-style clouds littered
throughout the room w/ space created between the panels ranging from 1'-0" ~
4'-0" 'open' space.  Structure above is steel joist - approximately 3'-0"
clearance from top of panel to bottom of decking.  I do not believe these
panels fall under the "Drop-out Ceiling" section... therefore, I'm wondering
if my spacing would be to place deflector within 6" of the deck and place
around / near the openings created between the panels.  Any thoughts,
previous experiences?  Knowledge from the forum is always appreciated!!

Chuck 



_______________________________________________
Sprinklerforum mailing list
[email protected] 
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 

To Unsubscribe, send an email to:[EMAIL PROTECTED] 
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to