I agree 100% Jim.

On 8/23/07, [EMAIL PROTECTED] <[EMAIL PROTECTED]> wrote:
> Craig:
>
> I wasn't saying a pre-action sprinkler system instead of a wet pipe system.
> My preference is a wet system with independent smoke sensors tied to the
> fire alarm system.   The only time I use pre-action is when the owner is
> the nervous type.
>
> Otherwise, the water damage can be greater due to potential operation of
> more heads due to the operational delay.
>
> Regards,
>
> James L.(Jim) Roberts, PE, SET
> Fluor Corporation
> 100 Fluor Daniel Drive - C104F
> Greenville, SC 29607
> 864.281.5149
> 864.281.4916(Fax)
>
>
>
>
>                        <[EMAIL PROTECTED]>
>                        Sent by:
>                        [EMAIL PROTECTED]                                      
>                                             To
>                        prinkler.org                         
> <[email protected]>
>                        08/23/2007 11:07 AM                                    
>                                                        cc
>                        Please respond to
>                        sprinklerforum                                         
>                                                   Subject
>                                                             RE: Carbon 
> Dioxide System Discharge Time
>
>
>
>
>
>
>
>
>
>
>
> Can the room be occupied at any time either by service personnel or
> other occasional operators?  Typically the answer would be yes as all
> equipment needs human intervention at some time.
>
> What Jim is saying is that a Pre-action sprinkler system would actually
> be the best choice and the most cost effective with something like
> FM-200 as the next choice instead of CO2.  There are some serious life
> safety issues you must consider when using CO2 in potentially occupied
> spaces.
>
>
>
> Craig L. Prahl, CET
> Fire Protection Group
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [EMAIL PROTECTED]
> http://www.lg.com
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Reza
> Esmaeili
> Sent: Thursday, August 23, 2007 10:59 AM
> To: [email protected]
> Subject: Re: Carbon Dioxide System Discharge Time
>
> Jim,
>   I forgot to explain, the room doesn't have any operators at all, and
> carbon dioxide is the best choice.
>   Thanks,
>   Reza
> [EMAIL PROTECTED] wrote:
>   Reza:
>
> I would not recommend a CO2 system as it is potentially too dangerous. I
> would consider a clean agent sytem per NFPA 2001.
>
> Hopefully, this is only a back-up to a wet pipe system, which is still
> my favorite.
>
> Regards,
>
> James L.(Jim) Roberts, PE, SET
> Fluor Corporation
> 100 Fluor Daniel Drive - C104F
> Greenville, SC 29607
> 864.281.5149
> 864.281.4916(Fax)
>
>
>
>
> Reza Esmaeili
>
> Sent by: To
> [EMAIL PROTECTED] [email protected]
> prinkler.org cc
> 08/23/2007 10:18 AM
> Please respond to Subject
> sprinklerforum Carbon Dioxide System Discharge Time
>
>
>
>
>
>
>
>
>
>
>
> Hi all,
> For designing a total flooding high pressure carbon dioxide system in a
> 3,500 cubic feet computer room with electrical equipment and cable runs,
> I have specified my room as "Dry electrical hazard" with flooding factor
> of
> 0.083 lb/cubic.feet and 50% design concentration according to NFPA-12.
> My questions are as below:
> 1)- Is a computer room fire a deep seated fire?
> 2)- NFPA 12 states that "For deep-seated fires, the design concentration
> shall be achieved within 7 minutes, but the rate shall be not less than
> that required to develop a concentration of 30 percent in 2 minutes." Is
> it a problem if the total discharge time would be only 1 minute for this
> case?
> Many thanks for your help in advance.
> Reza
>
>
> ---------------------------------
> Pinpoint customers who are looking for what you sell.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> ------------------------------------------------------------
> The information transmitted is intended only for the person or entity to
> which it is addressed and may contain proprietary, business-confidential
> and/or privileged material.
> If you are not the intended recipient of this message you are hereby
> notified that any use, review, retransmission, dissemination,
> distribution, reproduction or any action taken in reliance upon this
> message is prohibited. If you received this in error, please contact the
> sender and delete the material from any computer.
>
> Any views expressed in this message are those of the individual sender
> and may not necessarily reflect the views of the company.
> ------------------------------------------------------------
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
>
>
> ---------------------------------
> Looking for a deal? Find great prices on flights and hotels with Yahoo!
> FareChase.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> ------------------------------------------------------------
> The information transmitted is intended only for the person
> or entity to which it is addressed and may contain
> proprietary, business-confidential and/or privileged material.
> If you are not the intended recipient of this message you are
> hereby notified that any use, review, retransmission, dissemination,
> distribution, reproduction or any action taken in reliance upon
> this message is prohibited. If you received this in error, please
> contact the sender and delete the material from any computer.
>
> Any views expressed in this message are those of the individual
> sender and may not necessarily reflect the views of the company.
> ------------------------------------------------------------
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>


-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to