Richard,
  Many thanks for your great explanation. I think my previous question about 
selecting of fire pumps was a bit confusing, so I revised it as below.
  - Actually this is for a big deluge system, not sprinkler system, I mistyped 
sprinkler system in my previous email.
  Let me ask my question in another way. I want to asume 3 scenarios for 
selecting fire pumps for a water demand of  3900 GPM at 90 Psi.
  1- Want to be economical and and I don't afford to buy reserve pumps: (is it 
allowed as per NFPA not to have reserve pumps)?
  1-1: I have a very reliable power source: I will buy only an electric driven 
main fire pump 3500GPM at 102 psi working at about 112% of rated capasity ( I 
won't buy diesel, because I have a reliable power source and also I want to be 
economical)
  1-2:I doN't have a reliable power source: I will buy only a diesel fire pump 
3500GPM at 102 psi to work as my main fire pump.
   
  2- have too much money, I will buy reserve pumps:
  2-1: I will buy a main electric pump 3500GPM at 102 psi and a diesel pump 
3500GPM at 102 psi and my eletric fire pump would be main pump and diesel pump 
would be reserve pump which will work at power failure conditions.
  2-2: is above arrangement as per NFPA? or I should arrange diesel pump as 
main?
   
  3- Want to be very very  economical: I don't want to buy expensive pumps like 
Pattreson, Peerless, ... who are producing big pumps, I want to be very 
economical and buy the cheap pumps from my supplier who can't make a 3500 GPM 
pump, so I have to split the pumps and buy two sets of 1500 GPM at 129 psi 
working at about 130% or rated capacity.
  3-1: I have a very reliable power source: I will buy 2 electric pumps each 
1500 GPM at 129 psi working as main pumps.
  3-2: I doN't have a reliable power source: I will buy 2 diesel pumps each 
1500 GPM at 129 psi working as main pumps.   3-3: I am not 100% sure about 
reliability of power source: I will buy one electric pumps and one diesel pump 
at the same capacity of 1500 GPM at 129 psi, electric pump will start first and 
when water demand exceeds than 1500 GPM, then diesel pump will start, this 
arrangement is because in case of power failure, I can supply at least 50% of 
water demand to control half of fire. I know this is not logical, but imagine 
that power failure possibility is less than 1%.

   
  Would you kindly please analyze these three scenarios and let me know if any 
of them is aganist NFPA? If you have to choose one economical choice (among 
item 1) and one non economical choice (among item 2), and one very economical 
choice (among item 3), which ones you will choose? 
   
  Many thanks for your kind help in advance.
  Thank,
  Reza
  

Richard Malek <[EMAIL PROTECTED]> wrote:
  Reza,
In my industrial experience, I've never quite seen what you are proposing.
You have a couple issues I think you are trying to address -

Basic NFPA requirement - single automatic water supply; in your case, most
simply a single pump with a single water supply; in that case, personally, I
would start by looking at a single 3500 or 4000 gpm pumps(using the pump at
110-135% of rated is OK); I'm not sure why you would split that into two 50%
pumps; in the few cases where 50% pumps have been used in my experience ,
3 - 50% pumps are used so that the loss of any one pump doesn't impact your
ability to supply demand. Also, using that arrangement doesn't buy that much
from an insurance perspective, since the 3 pumps are supplied by a single
water supply. Typically the key issue for underwriters is redundant WATER
SUPPLIES, not necessarily pumps when those are required. So if there is no
owner or insurance underwriter requirement requiring two supplies, I would
start with the single pump arrangement to meet your demand and I would be
looking at making a 3500 or 4000 gpm pump work if possible. Your 90 psi
requirement isn't that high, so you've got some room to work with at churn
and be able to use at 110-135% of rated. HP requirement for those pumps will
be in the 350 HP +/- range. Iterate your selection between keeping the curve
flat as possible without making a costly jump in motor/engine sizing.
Diesels are available from typical suppliers, Clarke (JD), Cummins Fire
Power.

I have made two water supplies work to supply a single large demand if the
owner, underwriter doesn't require redundant supplies. That is developing a
combined supply and designing the sprinklers, water spray, etc. to that
supply. I usually don't start with that in a greenfield scenario - usually
existing where a new large demand is somewhat greater than what either
single supply can provide and it is far more cost effective than upgrading
either supply.

Electric vs. diesel depends on electrical power reliability and again if the
owner or insurance underwriter have a position on it. You would have to
estimate electrical vs. diesel drive costs if electric drive is an option, I
think you need the estimates to be accurate.

If you are actually required to install redundant pumps on a single water
supply or two pumps on redundant water supplies, typical arrangement is one
electric drive and one diesel drive or two diesel drives. These both would
be 100% pumps.

Just one last quick comment. 4600 gpm is a pretty large demand and in my
experience would be industrial deluge system related. If you are working
with a large industrial site, I always look at potential demands, not just
what happens to be the largest demand associated with the current pump
install. That would be a discussion with the owner typically since they need
to support the larger pump install. My experience would indicate if this is
an industrial application, a pair of 4000-5000 gpm pumps would be installed
off two water supplies. Pressure rating would be basically to limit
underground mains to 125-150 psi max.

Hope this helps,
Rich

Richard Malek
[EMAIL PROTECTED]


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of Reza
Esmaeili
Sent: Sunday, September 02, 2007 7:37 AM
To: [email protected]
Subject: Fire Pump Selection


Hi friends,
The estimated water demand for a sprinkler system and hose stream is 4600
GPM at 90 Psi, I want to select 2 x 2500 GPM at 90 psi pumps.
I know that electric fire pumps are duty pumps and diesel fire pumps are
standby pumps and will run in power failure situation. If I have to use 2 x
2500 GPM electric pumps as duty pumps and 2 x 2500 GPM diesel fire pumps as
standbuy pump, it will cost me too much. Is using of diesel fire pumps
necessary for all fire sprinkler systems as per NFPA-20?
I think I should better use 1 x 2500 GPM electric fire pump and 1 x 2500
GPM diesel fire pump, however in this case my diesel fire pump will not be
as an standby pump and will run when water demand exceeds than 2500 GPM. is
it a right arrangment as per NFPA-20?
What about If I use 2 x 2500 GPM electric fire pump, is it against
NFPA-20?
What is the best arrangment to according NFPA and also economical?
Thanks in advance for your kind help,
Reza


---------------------------------
Sick sense of humor? Visit Yahoo! TV's Comedy with an Edge to see what's on,
when.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


       
---------------------------------
Boardwalk for $500? In 2007? Ha! 
Play Monopoly Here and Now (it's updated for today's economy) at Yahoo! Games.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to