Remember it's the guy with the most paper that's coming out ahead when the
disputes start.  I cannot stress the importance of excellent (not just good)
communications and the way to make that happen is an RFI (Request for
Information). When it comes to something as significant as having to provide
12 fire service mains versus 1 it ought be in writing.  And stay within your
area of expertise. Something as important as if its one building or many
buildings can only be answered by one entity, the government AHJ. While what
I wrote may serve as guidance its only as good as you're AHJ seeing it that
way. If you have a formal written determination that's money in the bank.

Lastly contracting should not be a roll of the dice. It often amazes me to
have contractors arguing an issue that clearly deserves compensation only to
find out they signed on to some assumption without first hedging that bet.
The administrative side of the business deserves equal if not better
attention as the technical side.

In about one hour I am off to a meeting with a very astute architect who
says "I want to know what I'm getting into before I get there". No truer
words could be spoken.

John Drucker
Fire Protection Subcode Official (AHJ)
Former Project Manager-Siemens Fire Safety.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron Greenman
Sent: Tuesday, September 11, 2007 10:24 PM
To: [email protected]
Subject: Re: what makes a "building"

John,

That's a great answer as far as it goes. I'd like to add, for Garth's
benefit, that these types of determinations are in the realm of
responsibility for the architects and engineerrs and not the fire
sprinkler contractor. If at the point of the project that a sprinkler
contractor has been issued a notice to proceed (accompanied by the
standard engineering plans and specifications: "Design/build a
sprinkler system per NFPA 13 and local codes"), and the jurisdiction
has agreed with the architect that this arrangement is indeed a single
building, and that the arrangement of single riser is acceptable as
described, then the sprinkler contractor should proceed as though the
arrangement is correct. Certainly he wouldn't question whether there
was adequate glazing area or if HVAC calculations were correct, but if
he does feel that the arrangement is not correect then he should
register his concern, in writing, with his employer (probably the mech
sub or GC) and proceed. The GC should kick this concern up to his
employer, the architect, who should review the issues and determine
whether the original concept is sound or not. If none of this happens
then negligence does not rest with the sprinkler contractor but with
one of other, higher parties in the chain.

On 9/11/07, John Drucker <[EMAIL PROTECTED]> wrote:
>
> A question without a simple answer. From the building code a building is
> merely defined as " Any structure used or intended for supporting or
> sheltering any use or occupancy".  That in itself defines the difference
> between a building and a structure.  A home is a building, a radio
> transmission tower a structure.
>
> With that said a covered mall is an example of a large multiuse single
> building. Don't let the zoning issues steer you astray, theres no telling
> what some land use law could allow. It is entirely possible that a
building
> could project over or require access through another lot, a deeded
easement
> is just one method to do this. The building code actually makes reference
> that land use, i.e. zoning issues are outside the scope of the building
> code.
>
> If one desires to use the term building in the context of the building
code
> they must do so in complete compliance with the building code. Its simply
> not acceptable to pick and choose the sections "that work".  With that
said
> in order for this complex of buildings to be considered a single building
> the full width and breadth of the building code need be applied.
>
> First determine the occupancy (and more specifically the most stringent
> occupancy) construction type, height and area. Add the building areas
(also
> referred to as the footprint) together.  This represents the total
building
> area just as we would do with a single large building. Now take all of
this
> information and review it utilzing Table 503 of the IBC. Can we build this
> building in accordance with the table ?.  Either yes or no we must
consider
> the two modifiers that modify the tabular (the numbers found in the table)
> height and area limitations. Fire Sprinklers and Open Frontage are two
such
> modifiers, verify if using either or both of these modifiers allows the
> building to fall within the permissable (tabular + modifiers) building
area.
> This is essentially what 2006 IBC 503.1.2 (Buildings on same lot) says.
>
> If the "building" in question has passed muster so far, then means of
> egress(IBC Chapt 10) (number of exits, travel distance, etc) must be
> considered.  Next consider the fire protection requirements (IBC Chapt 9)
> (Sprinklers, Standpipes, Fire Alarms) .......  I think everyone gets the
> idea and its not a simple process.  As a code official when this question
> arises it is the design professional who must prove compliance not the
other
> way around.  A single large building will actually gravatate to a more
> stringent construction type, means of egress and fire protection. (just to
> name a few).
>
> There is one example I'd like to share and that has to do with occupant
> load. The IBC (2006 IBC 1004.2 for those who want to check) stipulates a
> provision wherein the occupant load of a building may be increased beyond
> that listed in the "Maximum Floor Area Allowances Per Occupant" Table
> (1004.1.1). But to do this the designer is directed by the code section
that
> "all other requirements of the code are also met".  In other words theres
a
> synergy implied in the code. If you want a glass of milk (versus say a
glass
> of water) you need to buy the whole cow.  So no picking and choosing.
>
> Hope that sheds some light on the whole thing. PS- Don't leave out the
> requirements of NFPA-13,14, 20............
>
> John Drucker
> Fire Protection Subcode Official
> Building Inspector
> New Jersey
>
> Safe Buildings Save Lives !
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>


-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to