Carig,
  Thanks for your email, in the example you mentioned, for an Ordinary Hazard 
Group II occupancy with a design area of 1,500 sq. ft. and density of 0.20 gpm 
sq,  I agree that my theorical sprinklers demand is 300 Gpm and my theorical 
hose demand is 250 Gpm, so if I should assume 2 fire boxes active and from my 
hydraulic calculations I concluded that for example flow rate for first fire 
box is 142 Gpm and second is 156 Gpm, So the total demand for hose streams is 
(142+156) =295 Gpm. As 295>250 so it is ok, and I should assume 295 Gpm as my 
real hose streams.
  If for my application I assume 12 active sprinklers and from my hydraulic 
calculations I conclude that my real sprinklers demand is 323 Gpm.
  Then my sprinklers and hose streams demand would be 323 + 295 = 618 Gpm, this 
is the real demand, not theorical demand, and I should select my pump and water 
tank capacity  based on 618 Gpm not a theorical of 550 Gpm, I am right?
Why didn't you included any external hydrants demands in calculating the total 
demand? did you assume that in no case a hydrant will work with sprinklers and 
fire boxes at the same time? Why?
  Thanks,
  Reza

[EMAIL PROTECTED] wrote:
  Reza, 

You first need to establish the design criteria for your facility. So
let's say it's just a factory as you stated and they do mostly machining
type work, no special hazards or anything like that, we can take a look
in NFPA 13 (2007), in A.5.3.2 and we'll see that we would have an
Ordinary Hazard Group II occupancy. Then go to Figure 11.2.3.1.1
(Density/Area Curves) and you will see that for an Ordinary Hazard Group
II you could have a density of 0.20 gpm sq. ft with a design area of
1,500 sq. ft. In Table 11.2.3.1.2 For OH II your hose stream allowance
is 250 gpm. So .20 gpm/sf x 1,500 sf give you 300 gpm sprinkler demand
plus 250 gpm hose gives you 550 total system demand. This is bare
minimum and it is often recommended to add at least 10%-15% to that
since we don't end up with exactly .20 gpm/sf from each head when
they're calculated. So with that in mind you could have a demand of
605-630 +/- gpm of system demand. 

For this application the head spacing could vary, say we used 130 sq. ft
per sprinkler (just for discussion) so in that 1,500 sq. ft you'd end up
calculating approximately 12 sprinklers. 

This is a real basic overview and not intended to include or encompass
every aspect of hydraulic calculations, system design or other
variables.






Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC 29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Reza
Esmaeili
Sent: Thursday, September 13, 2007 7:41 AM
To: [email protected]
Subject: Water demand for fire protection system!

Hi all,
I have a bit problem in calculating my water demand for a theory
project like below:
Assume that there is a factory protected with a wet pipe sprinkler
system, 4 fire boxes and 4 external hydrants on main ring.

According to NFPA-13 i conclude that for example I should consider 20
sprinklers active and from my hydraulic calculations I concluded that my
sprinklers demand would be 643 Gpm.

I also assumed 2 fire boxes active and from my hydraulic calculations
I concluded that for example flow rate for first fire box is 142 Gpm and
second is 156 Gpm, So the total demand for hose streams is (142+156) =
295 Gpm.

I also have 4 external hydrants on main ring, should I assume that at
least one hydrants will work at the same time with my sprinklers and 2
fire boxes? If the answer is yes, then I will active one hydrant and my
hydraulic calculations I concluded that my hydrant demand is 860 Gpm.

So I have following demands:
1- Wet pipe sprinkler system ------------------------------- Demand:
643 Gpm
2- Hose streams (Fire boxes) ------------------------------ Demand:
295 Gpm
3- External Hydrants on main ring------------------------- Demand: 860
Gpm
Now I conclude that my total water demand is (643 + 295 + 860 )= 1798
Gpm.
My questions are as below:
A- Should I assume that my external hydrants will work at the same
time with sprinklers and 2 fire boxes? and should I include them in
total water demand?
B- Should I assume exactly 295 Gpm for my hose streams? or NFPA has
standard for water demand of hose streams( Ex. 250 or 500 Gpm) ?
C- What is my right total demand in your idea?
I know that my questions may surprise you, becuase I am a beginner, I
would appreciate if you answer in details to know where I am wrong.
Thanks,
Reza


---------------------------------
Don't let your dream ride pass you by. Make it a reality with Yahoo!
Autos. 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


       
---------------------------------
Yahoo! oneSearch: Finally,  mobile search that gives answers, not web links. 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to