What John said two times over.

On 9/12/07, John Drucker <[EMAIL PROTECTED]> wrote:
>
> Remember it's the guy with the most paper that's coming out ahead when the
> disputes start.  I cannot stress the importance of excellent (not just good)
> communications and the way to make that happen is an RFI (Request for
> Information). When it comes to something as significant as having to provide
> 12 fire service mains versus 1 it ought be in writing.  And stay within your
> area of expertise. Something as important as if its one building or many
> buildings can only be answered by one entity, the government AHJ. While what
> I wrote may serve as guidance its only as good as you're AHJ seeing it that
> way. If you have a formal written determination that's money in the bank.
>
> Lastly contracting should not be a roll of the dice. It often amazes me to
> have contractors arguing an issue that clearly deserves compensation only to
> find out they signed on to some assumption without first hedging that bet.
> The administrative side of the business deserves equal if not better
> attention as the technical side.
>
> In about one hour I am off to a meeting with a very astute architect who
> says "I want to know what I'm getting into before I get there". No truer
> words could be spoken.
>
> John Drucker
> Fire Protection Subcode Official (AHJ)
> Former Project Manager-Siemens Fire Safety.
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Ron Greenman
> Sent: Tuesday, September 11, 2007 10:24 PM
> To: [email protected]
> Subject: Re: what makes a "building"
>
> John,
>
> That's a great answer as far as it goes. I'd like to add, for Garth's
> benefit, that these types of determinations are in the realm of
> responsibility for the architects and engineerrs and not the fire
> sprinkler contractor. If at the point of the project that a sprinkler
> contractor has been issued a notice to proceed (accompanied by the
> standard engineering plans and specifications: "Design/build a
> sprinkler system per NFPA 13 and local codes"), and the jurisdiction
> has agreed with the architect that this arrangement is indeed a single
> building, and that the arrangement of single riser is acceptable as
> described, then the sprinkler contractor should proceed as though the
> arrangement is correct. Certainly he wouldn't question whether there
> was adequate glazing area or if HVAC calculations were correct, but if
> he does feel that the arrangement is not correect then he should
> register his concern, in writing, with his employer (probably the mech
> sub or GC) and proceed. The GC should kick this concern up to his
> employer, the architect, who should review the issues and determine
> whether the original concept is sound or not. If none of this happens
> then negligence does not rest with the sprinkler contractor but with
> one of other, higher parties in the chain.
>
> On 9/11/07, John Drucker <[EMAIL PROTECTED]> wrote:
> >
> > A question without a simple answer. From the building code a building is
> > merely defined as " Any structure used or intended for supporting or
> > sheltering any use or occupancy".  That in itself defines the difference
> > between a building and a structure.  A home is a building, a radio
> > transmission tower a structure.
> >
> > With that said a covered mall is an example of a large multiuse single
> > building. Don't let the zoning issues steer you astray, theres no telling
> > what some land use law could allow. It is entirely possible that a
> building
> > could project over or require access through another lot, a deeded
> easement
> > is just one method to do this. The building code actually makes reference
> > that land use, i.e. zoning issues are outside the scope of the building
> > code.
> >
> > If one desires to use the term building in the context of the building
> code
> > they must do so in complete compliance with the building code. Its simply
> > not acceptable to pick and choose the sections "that work".  With that
> said
> > in order for this complex of buildings to be considered a single building
> > the full width and breadth of the building code need be applied.
> >
> > First determine the occupancy (and more specifically the most stringent
> > occupancy) construction type, height and area. Add the building areas
> (also
> > referred to as the footprint) together.  This represents the total
> building
> > area just as we would do with a single large building. Now take all of
> this
> > information and review it utilzing Table 503 of the IBC. Can we build this
> > building in accordance with the table ?.  Either yes or no we must
> consider
> > the two modifiers that modify the tabular (the numbers found in the table)
> > height and area limitations. Fire Sprinklers and Open Frontage are two
> such
> > modifiers, verify if using either or both of these modifiers allows the
> > building to fall within the permissable (tabular + modifiers) building
> area.
> > This is essentially what 2006 IBC 503.1.2 (Buildings on same lot) says.
> >
> > If the "building" in question has passed muster so far, then means of
> > egress(IBC Chapt 10) (number of exits, travel distance, etc) must be
> > considered.  Next consider the fire protection requirements (IBC Chapt 9)
> > (Sprinklers, Standpipes, Fire Alarms) .......  I think everyone gets the
> > idea and its not a simple process.  As a code official when this question
> > arises it is the design professional who must prove compliance not the
> other
> > way around.  A single large building will actually gravatate to a more
> > stringent construction type, means of egress and fire protection. (just to
> > name a few).
> >
> > There is one example I'd like to share and that has to do with occupant
> > load. The IBC (2006 IBC 1004.2 for those who want to check) stipulates a
> > provision wherein the occupant load of a building may be increased beyond
> > that listed in the "Maximum Floor Area Allowances Per Occupant" Table
> > (1004.1.1). But to do this the designer is directed by the code section
> that
> > "all other requirements of the code are also met".  In other words theres
> a
> > synergy implied in the code. If you want a glass of milk (versus say a
> glass
> > of water) you need to buy the whole cow.  So no picking and choosing.
> >
> > Hope that sheds some light on the whole thing. PS- Don't leave out the
> > requirements of NFPA-13,14, 20............
> >
> > John Drucker
> > Fire Protection Subcode Official
> > Building Inspector
> > New Jersey
> >
> > Safe Buildings Save Lives !
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email to:[EMAIL PROTECTED]
> > (Put the word unsubscribe in the subject field)
> >
>
>
> --
> Ron Greenman
> at home....
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>


-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to