Hi Travis! Nice to see you are writing to me again! NFPA says that "...The lower duration value is permitted where remote or central station waterflow alarm service is provided, then It is expected that the fire department or fire brigade will be made aware of the fire more quickly..." So if a central station waterflow alarm service is provided, then how many percent is permitted to reduce the water supply duration? I don't know why NFPA never made a relation between water supply duration and distance to local fire brigade . So it seems that the water supply durations stated in NFPA is to control water without help of local fire brigade. The above NFPA sentence confuses me, let me explain the reason of water supply duration in two way: 1- Water supply duration is NOT related to how much close the local fire brigade is, it depends to how much time it takes to control or extinguish fire based on hazard type, if the fire brigade department comes in only 3 minutes, they still need water to extinguish fire (they don't bring enough water), Carig, you said "You can not guarantee that the fire will be controlled in only 45 minutes regardless of how soon the local fire brigade responds" So If duration is not related to distance to local fire brigade, so why NFPA says above statement and allow to reduce duration? 2- Water supply duration IS related to how much close the local fire brigade is, however no one can guarantee if the local fire brigade will come in less than 5 minutes, but when they come sooner they will help sprinkler system and the fire would be controlled soon and less duration is needed, so usually factories which are nearer to local fire brigade need less water. If sprinklers can extinguish fire in 90 minutes without help of fire brigade department, then sprinklers with the help of local fire brigade may extinguish water 45 minutes, the sooner local fire brigade comes, the sooner water is controlled, right? I don't know which theory is right, may be no one! what is the right theory in your opinion? Thanks, Reza
[EMAIL PROTECTED] wrote: Duration is critical. You can not guarantee that the fire will be controlled in only 45 minutes regardless of how soon the local fire brigade responds. Plus, are you relying on them to bring additional water if needed? Their supply within the trucks is very limited so as they run out they may have to leave the site to refill but in any case that could result in a delay in their attack and an out of control fire scenario. I would never for any reason see the reduction of the duration as specified in NFPA having any value. Quite the contrary, it would result in a non-compliant system and put you responsible for any damage due to the ineffectiveness of the inadequate system. In the building codes we have there is wording stating that even if a particular fire system is not required by the code, if you install it, you must still install it according to the applicable codes. So even if no one was going to review or approve it, you must still design and install it according to the codes that govern it. Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.lg.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Reza Esmaeili Sent: Tuesday, September 25, 2007 10:52 AM To: [email protected] Subject: How much Water Supply Duration is Important? Hi, I know it is very important to take care of water supply duration, but how much important? Imagine fire brigade is very close to the factory and will come to extinguish fire in less than 5 minutes. If for an extra hazard occupancy which I need at least 90 minutes of water supply for my wet pipe sprinkler system demand, I reduce it to 45 minutes, then what will happen? If I don't care about my required pressure and flow, then the entire system will fail, but if I reduce water supply duration, then system will work properly but only for 45 minutes, so if the fire brigade can come in 5 minutes, there wouldn't be a serious problem, Imagine that no one is going to approve the system (No insurance, ...). I just want to analyze fire behaviour in this case, it is not a real project. Thanks, Reza --------------------------------- Be a better Globetrotter. Get better travel answers from someone who knows. Yahoo! Answers - Check it out. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) --------------------------------- Yahoo! oneSearch: Finally, mobile search that gives answers, not web links. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)