Ron,

This is where I see the real problem.

If you are not the "Engineer of Record", should you be the one making the Commodity Class determination?

Do you realy want that liability if you are not an engineer?


Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

This e-mail and any attachments are CONFIDENTIAL and may be protected by one or more legal privileges. It is intended solely for the use of the addressee identified above. If you are not the intended recipient, any use, disclosure, copying or distribution of this e-mail is unauthorized. If you received this e-mail in error, please notify the sender immediately at the above captioned address. ----- Original Message ----- From: "Russell" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Tuesday, September 25, 2007 9:42 AM
Subject: RE: Automobile dealership parts storage


Well, this is really where the problem is at the moment. The AHJ is
requesting the class of commodity in order to complete his review of our
drawings; therefore, it's being dumped back on me. But even it wasn't, I
still need to know how to treat situations like this that may arise in the
future.

Ron

Internal Virus Database is out-of-date.
Checked by AVG Free Edition.
Version: 7.5.467 / Virus Database: 269.8.13/843 - Release Date: 6/10/2007
1:39 PM


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to