Hello Forum,
I have a situation where a city is requiring 4800 gpm to be flowed @ a min of 20 from all hydrants within 500 ft of the bldg. This particular bldg has 5 hydrants on a 12" city line. I have received a flow test of 96-S 64-R 2519-GPM and set all five hydrants to flow 960 GPM. This will not produce the requirement. We do have a pump being installed inside the bldg.(2000 GPM / rated pressure of 60). If I pipe out from the pump room and add hydrants around the bldg. I still cannot meet this requirement. Has anyone run into this problem or had a similar situation? Any suggestions? Bobby Gillett Project Manager [EMAIL PROTECTED] (731)-424-0130 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)