Thanks,

That was the outcome that I had came up with, but didn't want to bump heads
with the AHJ until I had received some feed back from experience. Just in
case I was missing something and to see how some of you might have handled
this.

Again thanks to all!!

Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mark
Hasenmyer
Sent: Wednesday, October 03, 2007 8:05 AM
To: [email protected]
Subject: RE: Fire Flow requirements

You can't get 4800-gpm at 20-psi with that flow test, no matter what you do
(the best you can do is 4018-gpm); and you can't get 4800-gpm through that
fire pump, no matter what you do.  The city wants their Needed Fire Flow for
the building and there are several methods to figure the NFF but most
municipalities get it from a chart in the IFC.  I had a project where the
water supply from the city was not adequate to meet the NFF for the project.
The only thing to do is to store water or get a variance.

Mark Hasenmyer, PE
MEH Fire Protection Engineering LLC
1311 River Oaks Drive
Flower Mound, TX 75028
Office (972) 874-2662
Fax (972) 874-5591


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bobby Gillett
Sent: Wednesday, October 03, 2007 7:14 AM
To: [email protected]
Subject: Fire Flow requirements

Hello Forum,

 

I have a situation where a city is requiring 4800 gpm to be flowed @ a min
of 20 from all hydrants within 500 ft of the bldg. This particular bldg has
5 hydrants on a 12" city line. I have received a flow test of 96-S 64-R
2519-GPM and set all five hydrants to flow 960 GPM. This will not produce
the requirement. We do have a pump being installed inside the bldg.(2000 GPM
/ rated pressure of 60). If I pipe out from the pump room and add hydrants
around the bldg. I still cannot meet this requirement. Has anyone run into
this problem or had a similar situation? Any suggestions?  

 

Bobby Gillett

Project Manager

[EMAIL PROTECTED]

(731)-424-0130

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to