That's only in a storage type requirement. 
In a congested valve district they require 12,000 plus 3,000 for a second
fire.
In a Haz. Occupancy (no reduction listed for sprinklers) they range from
5,000 for minor hazard, 10,000 for moderate haz., and 15,000 for major!!!
Of course they also have less demanding requirements for non-storage
applications and dwellings.

Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ray Schmid
Sent: Wednesday, October 03, 2007 1:13 PM
To: [email protected]
Subject: RE: Fire Flow requirements

They may want to save everyone the trouble and just ban non-sprinklered
buildings.  I don't know of too many municipalities that can deliver
8,000 gpm even at 20 psi (or 5,600 gpm for that matter) That's an awful
lot of water and seems pretty excessive.  What type of fire are they
preparing to fight, Ground Zero?

Ray Schmid
Koffel Associates

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bobby
Gillett
Sent: Wednesday, October 03, 2007 12:24 PM
To: [email protected]
Subject: RE: Fire Flow requirements

Still haven't heard from the AHJ to ask the obvious, but looking at his
Fire
Flow Requirements Chart there is already a reduction for sprinklered
buildings. This particular scenario; No Sprinklers=8,000 GPM  Sprinkler
System=5,600  ESFR=4800!!! Maybe he will allow a 50% reduction-then I
will
be in the game.

Thanks again to EVERYONE for their help. I will let you know how it
plays
out. 

Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Wednesday, October 03, 2007 8:54 AM
To: [email protected]
Subject: RE: Fire Flow requirements

I deal with this problem everyday here in Phoenix. Table B105.1 list the
required fire flows based on total square feet of the largest building
on a site. B105.2 Exception allows up to a 50% reduction in fire flow
for buildings sprinklered in accordance with 903. It doesn't sound like
the AHJ has allowed a reduction for sprinklers so I would first ask that
they reconsider the requirement and apply the allowed 50% reduction.

Where is the 500 ft dimension coming from? 508.5.1 Requires private
hydrants if all portions of a facility are not within 400 ft. of a
(public) hydrant on an access road so 500 ft. is pushing the envelope.

Good luck and please let me know how this ends.

Ron Fletcher
Aero Automatic
Phoenix, AZ  

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bobby
Gillett
Sent: Wednesday, October 03, 2007 5:14 AM
To: [email protected]
Subject: Fire Flow requirements

Hello Forum,

 

I have a situation where a city is requiring 4800 gpm to be flowed @ a
min of 20 from all hydrants within 500 ft of the bldg. This particular
bldg has
5 hydrants on a 12" city line. I have received a flow test of 96-S 64-R
2519-GPM and set all five hydrants to flow 960 GPM. This will not
produce the requirement. We do have a pump being installed inside the
bldg.(2000 GPM / rated pressure of 60). If I pipe out from the pump room
and add hydrants around the bldg. I still cannot meet this requirement.
Has anyone run into this problem or had a similar situation? Any
suggestions?  

 

Bobby Gillett

Project Manager

[EMAIL PROTECTED]

(731)-424-0130

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to