So any of the choices discussed in the '07 complies for big systems.  4
heads manifold on a HPS system is 40 seconds.  What's interesting is then
systems under 750 might have a problem.  They comply with 13 but maybe not
IBC/NJ.

Chris 
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John Drucker
Sent: Thursday, October 11, 2007 2:16 PM
To: [email protected]
Subject: RE: Dry system size

>Now local amendments are another thing but one should check for ANY and
all such headaches.<

IBC/NJ 903.5.1 "Dry Pipe Systems shall deliver water to the inspectors
test pipe in not more than 60 seconds."

John Drucker
Fire Protection Subcode Official
Red Bank, NJ


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Thursday, October 11, 2007 1:30 PM
To: [email protected]
Subject: Re: Dry system size

I think it was the old BOCA code that required it but I don't think
there is anything in the IBC.  Anyone else seen it in there (or maybe
the IFC).  Now local amendments are another thing but one should check
for ANY and all such headaches.

Roland

On Oct 11, 2007, at 10:01 AM, Mike Brown (TECH- GVL) wrote:

> Let me say again, you might want to check with the AHJ because many of

> them and some of the building codes still requiring a one head test 
> and you must get the water to the ITC in 60 seconds.  You can engineer

> it all you want but it will boil down to what the code and the AHJ 
> requires.
> Michael L. Brown
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Roland 
> Huggins
> Sent: Thursday, October 11, 2007 12:39 PM
> To: [email protected]
> Subject: Re: Dry system size
>
> reread the last sentence of 7.2.3.7. for confirmation of what I said
>
> Roland
>
> On Oct 11, 2007, at 8:50 AM, Russell wrote:
>
>> So if I choose option #3, I do not have to use option #2 involving a 
>> program or use #1 and meet it's requirement of a single connection 
>> with 60 sec. time period. #3 means using a test manifold using table 
>> 7.2.3.6.1. This table shows (in my situation for ordinary hazard) to 
>> use a two outlet manifold utilizing one branch line and a water 
>> delivery time of 50 seconds.
>>
>> Ron
>>
>>
>>
>> -----Original Message-----
>> From: [EMAIL PROTECTED]
>> [mailto:[EMAIL PROTECTED] On Behalf Of Roland

>> Huggins
>> Sent: Thursday, October 11, 2007 11:16 AM
>> To: [email protected]
>> Subject: Re: Dry system size
>>
>> lets start over again and allow me to summarize what has been said by

>> others.
>>
>> For systems greater than 750 gals, you have THREE options.
>> 1. Single test connection at 60 seconds 2. Calculated delivery using 
>> Table 7.2.3.6.1 3. Test manifold using Table 7.2.3.6.1
>>
>> Read 7.2.3.7 taking note of the last sentence (confirming if you use 
>> the manifold you do not have to do either of the other two options).
>> This section also tells you where to connect when more than 2 
>> sprinklers are on the manifold.
>>
>> Other tidbits:
>> Even with a calculated system, you still have to do the single head 
>> flow test as part of the acceptance test BUT there is NO 60 sec 
>> limit.
>> For smaller systems serving a dwelling unit, you now have to satisfy 
>> the 60 sec rule (for spray sprinklers).
>>
>> Roland
>>
>> On Oct 10, 2007, at 1:45 PM, Russell wrote:
>>
>>> I take it that the table 7.2.3.6.1 goes only with a program, but if 
>>> so, how do I determine the number of branch lines to include in the 
>>> manifold? Am I not understanding what you're telling me?
>>>
>>> Ron
>>>
>>> Internal Virus Database is out-of-date.
>>> Checked by AVG Free Edition.
>>> Version: 7.5.467 / Virus Database: 269.8.13/843 - Release Date:
>>> 6/10/2007
>>> 1:39 PM
>>>
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>> To Unsubscribe, send an email to:Sprinklerforum- 
>>> [EMAIL PROTECTED] (Put the word unsubscribe in the subject 
>>> field)
>>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email to:Sprinklerforum- 
>> [EMAIL PROTECTED] (Put the word unsubscribe in the subject 
>> field)
>>
>> Internal Virus Database is out-of-date.
>> Checked by AVG Free Edition.
>> Version: 7.5.467 / Virus Database: 269.8.13/843 - Release Date:
>> 6/10/2007
>> 1:39 PM
>>
>>
>> Internal Virus Database is out-of-date.
>> Checked by AVG Free Edition.
>> Version: 7.5.467 / Virus Database: 269.8.13/843 - Release Date:
>> 6/10/2007
>> 1:39 PM
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email to:Sprinklerforum- 
>> [EMAIL PROTECTED] (Put the word unsubscribe in the subject 
>> field)
>>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:Sprinklerforum- 
> [EMAIL PROTECTED] (Put the word unsubscribe in the subject 
> field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to