The entire 2006 IBC/NJ Edition is viewable online free of charge at; http://www2.iccsafe.org/states/newjersey/
John Drucker Fire Protection Subcode Official Red Bank, NJ -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Roland Huggins Sent: Thursday, October 11, 2007 4:03 PM To: [email protected] Subject: Re: Dry system size to state the obvious - that is NOT from the model code but a NJ amendment Roland On Oct 11, 2007, at 12:15 PM, John Drucker wrote: >> Now local amendments are another thing but one should check for >> ANY and > all such headaches.< > > IBC/NJ 903.5.1 "Dry Pipe Systems shall deliver water to the inspectors > test pipe in not more than 60 seconds." > > John Drucker > Fire Protection Subcode Official > Red Bank, NJ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)